[Equest-users] CHW error message
Robby Oylear
robbyoylear at gmail.com
Thu Dec 15 13:27:50 PST 2011
Varkie,
Your leaving supply air temperature off the coil must be 6 degress higher
than your chilled water supply temperature. If your unit fan is in the
draw through configuration, the leaving temperature off of your coil will
need to be your design supply air temperature minus the fan motor heat gain.
For example, if you have a leaving air temperature of 55 deg F out of the
unit and a fan motor heat gain of 3 deg F, then in a draw through
configuration, your leaving coil temperature would be 52 deg F which means
a maximum chilled water supply temperature of 46 deg F. If you switched
the fan to blow through, then the maximum chilled water supply temperature
would be 49 deg F.
Does that answer your question?
-Robby
On Thu, Dec 15, 2011 at 1:27 PM, Varkie C Thomas <thomasv at iit.edu> wrote:
> What causes the error below? The CHW input used all eQUEST defaults. The
> bldg is high-rise residential. The systems used defaults also (4-pipe FCU).
> Varkie Thomas
>
> pro Maslak sim
> DOE-2.2-47h2 12/15/2011 15:03:51 BDL RUN 7******
>
>
> ****
>
> REPORT- ATTN Simulation Messages For Review HVAC Program
> WEATHER FILE- EPW ISTANBUL,-,TUR ****
>
>
> ---------------------------------------------------------------------------------------------------------------------------------
> ****
>
> ** **
>
> ** **
>
>
> ***ERROR***********************************************************************
> ****
>
> In EL1 Sys1 (FC) , cooling coil leaving
> temperature must****
>
> be at least 6F higher than entering water temp.****
>
> ** **
>
>
> ***ERROR***********************************************************************
> ****
>
> In EL1 Sys1 (FC) , cooling coil leaving
> temperature must****
>
> be at least 6F higher than entering water temp.****
>
> ** **
>
>
> ***ERROR***********************************************************************
> ****
>
> In EL1 Sys1 (FC) , cooling coil leaving
> temperature must****
>
> be at least 6F higher than entering water temp.****
>
> ** **
>
>
> ***ERROR***********************************************************************
> ****
>
> ** **
>
> ** **
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111215/57cfc588/attachment-0002.htm>
More information about the Equest-users
mailing list