Yes it can. Depending on which deduction you are trying to achieve, the rules for modeling say you must include the base system type per ASHRAE Appendix G for the whole building area.
A 40,000 sqft renovation of a 200,000 sqft building can only achieve a deduction for 40,000 sqft, and if going after full deduct or systems deduct it must be compared to the ASHRAE baseline system type for a 200,000 sqft space.
If dealing with DES or CEP the rules change again.
Also, very important, the other systems of the building must comply with the mandatory provisions of ASHRAE 90.1 2001. If the 40,000 sqft is a net-zero energy consumer, but the rest of the building does not comply with the mandatory provisions of ASHRAE 90.1 2001 then the building can't qualify.
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer II
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com/>
[cid:image001.gif at 01CBD1AA.08DBA910]<http://www.tlc-engineers.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jim Olson
Sent: Sunday, February 20, 2011 7:34 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Remodels
Hi, can an addition to a building receive the tax deduction independent of the older existing building?
Jim Olson
Building Performance and Energy Specialist
E3 Coalition.org
304 S. Main St
Viroqua WI 54665
608-637-2499 (O)
608-632-4103 (C)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110221/0b5bb5ae/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110221/0b5bb5ae/attachment-0002.gif>
More information about the Equest-users
mailing list