Hm... I'll take a swing at this...
I'd suggest simply modeling a normal gas storage water heater.
1. Zero out the ambient tank heat losses in detailed edit (set
tank UA to 0)
2. Match burner efficiency (HIR) and capacity to the actual
equipment
3. Call it a day ;)
By default (coming out of the wizards), hot water loops don't have a
loop UA defined and so will not model losses. If you're trying to
differentiate between instantaneous and storage systems with a
static/recirc loop, your storage model ought to define something for
loop losses to keep everything on a level playing field.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Cantrill
Sent: Tuesday, February 22, 2011 2:38 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling gas instantaneous water heaters in
eQuest
I am working on a project that is using instantaneous gas water heaters.
What is the best way to model these in eQuest?
Thanks,
David Cantrill
Branch Manager - Mississippi
<http://www.cxgbs.com/>
CxGBS is not responsible for design concept, design criteria, compliance
with codes, design or general construction scheduling, cost estimating,
or construction management.
CONFIDENTIALITY NOTICE: This e-mail transmission, and any documents,
files or previous e-mail messages attached to it may contain
confidential information that is legally privileged. If you are not the
intended recipient or the person responsible for delivering it to the
intended recipient, you are hereby notified that any disclosure,
copying, distribution or use of any of the information contained in or
attached to this transmission is strictly prohibited. If you have
received this transmission in error, please immediately notify us by
telephone at (770) 831 6760 and destroy the original transmission and
its attachments without reading them. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110223/ce5e0e48/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110223/ce5e0e48/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 11281 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110223/ce5e0e48/attachment-0002.gif>
More information about the Equest-users
mailing list