[Equest-users] Converting Heat Pump COP to EIR
Ana N.
ananeddav at hotmail.com
Mon Jan 3 08:25:48 PST 2011
You can use this link to access discussion on this topic.
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-May/004407.html
Heating EIR = (1/(COP*3.413)-0.012167)/((1/3.413)-0.012167)
and
Heating EIR = (1/((HSPF*0.28+1.13)*3.413)-0.012167)/((1/3.413)-0.012167)
Hope this helps,
Ana
Date: Mon, 3 Jan 2011 08:12:26 -0800
From: kathryn.kerns at bceengineers.com
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Converting Heat Pump COP to EIR
Everyone, is there a relationship written down somewhere that removes fan energy from a heat pump COP value to develop a heating EIR? Something like the DX cooling EER equation that removes fan energy from EIR cooling values? It looks like the eQuest wizard is doing something like that when a heat pump heating COP is entered, but I am not sure what.
_______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/1db7723f/attachment-0001.htm>
More information about the Equest-users
mailing list