[Equest-users] Baseline HVAC Type - Table G3.1.1 A&B (90.1-2007)
Peter Hillermann
peterh at westallarchitects.com
Mon Jan 3 12:05:28 PST 2011
Jeff,
We tried separating one of our buildings like that and the comment we got
from USGBC was.
7. The Baseline system type modeled does not seem consistent with the system
mapping from Table G3.1.1A. Please
confirm that the Baseline system was modeled correctly, or revise the system
type to reflect ASHRAE modeling protocol. Nonresidential
buildings which are five floors or less and between 25,000 and 150,000
sq.ft. should be modeled with System Type
#5 (fossil fuel heating) or System Type #6 (electric heating).
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
Description: e-signatureDescription: USGBC-Logo
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Ross-Bain
Sent: Thursday, December 30, 2010 9:54 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B (90.1-2007)
Hi All,
If a building has an overall area greater than 25,000 sq ft, but has
distinct wings each less than 25,000 sq ft and each has independent HVAC
systems, would one use System 6 (overall) or use System 4 (based on each
wing) to determine baseline type?
Thanks,
Jeffrey G Ross-Bain, PE, LEED, BEMP
Ross-Bain Green Building, LLC
404-228-2893
P Build Green...Save Time
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/e9847aed/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/e9847aed/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/e9847aed/attachment-0001.jpeg>
More information about the Equest-users
mailing list