[Equest-users] Cooking Equipment and Elevators/ Exhaust fans
Bosch, Crina
CBosch at karpinskieng.com
Mon Jan 24 12:37:13 PST 2011
Thank you all for your suggestions and thoughts. I will try the option
with 2 meters and hopefully this will resolve my problem.
Sincerely,
Crina Bosch
________________________________
From: Ravi Srinivasan [mailto:ravi.s.srinivasan at gmail.com]
Sent: Monday, January 24, 2011 3:35 PM
To: Demba Ndiaye; Bosch, Crina
Subject: Re: [Equest-users] Cooking Equipment and Elevators/ Exhaust
fans
Well said, Demba.
Crina, create two new meters (of "building" type) - one for Kitchen and
another for Elevator. Input kW and associated schedules as direct loads.
Open the "utility" electricity meter (typically "EM1"). And, bring these
two newly created meters within EM1.
PS-B report should show energy use of Kitchen and Elevator separately.
Ensure you have these two meters and associated loads input in baseline
and proposed.
Best Regards.
--
Ravi Srinivasan, PhD
On Mon, Jan 24, 2011 at 3:15 PM, Demba Ndiaye <Demba.Ndiaye at setty.com>
wrote:
Crina,
For the elevators, you can create a separate meter...
_______________
Demba NDIAYE
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Monday, January 24, 2011 3:05 PM
To: Bosch, Crina; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cooking Equipment and Elevators/ Exhaust
fans
My only suggestion would be to perform a save-as and change the misc
equipment energy consumption to zero for the elevator (and then do it
again for the kitchen) to find the equipment usage and demand.
If your independent fans are exhaust fans, I would do the same thing
that I mentioned above.
The reports in eQUEST will not break out the equipment but you can write
a narrative explaining that eQUEST cannot separate these loads and
explain your procedure. I believe that the reviewer simply wants to make
sure that the energy consumption is the same for these items in the
baseline and proposed model.
From: Bosch, Crina [mailto:CBosch at karpinskieng.com]
Sent: Monday, January 24, 2011 2:04 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cooking Equipment and Elevators/ Exhaust fans
Dear users,
I received form USGBC the following comment:
"The project contains elevators and kitchen equipment in the actual
design; however, the process energy related to the elevator and kitchen
equipment was not included in each energy model, since Section 1.8 of
the template does not include the process energy consumption for
elevator or kitchen equipment. Revise the Proposed and Baseline models
to include the process energy for elevator and kitchen equipment in the
appropriate space in the models. In addition, update the template
reflecting the changes."
The kitchen equipment and elevators were input in the model under the
equipment tab for each space as designed but I couldn't separate them in
eQuest from the Misc. Equip under the Consumption by Enduse Report or
Demand Report. I verified everything I could and see how I can spit them
and the only thing I found was this: "INTERIOR-EU - Accepts a list of up
to 10 code-words specifying the end-use category of the INTERIOR-POWER.
The code-words correspond to the end-use categories in the end-use
reports (PS-E, PS-F, BEPS, BEPU). Acceptable entries are LIGHTS,
TASK-LIGHTS, MISC-EQUIP, SPACE-HEATING, SPACE-COOLING, HEAT-REJECT,
PUMPS&AUX, VENT-FANS, REFRIG-DISPLAY, HT-PUMP-SUPPLEM, DOMEST-HOT-WTR,
and EXT-USAGE. "
In the end I understand that eQuest does not have the option of doing
what the reviewer is asking for.
The reviewer also wants the independent fans to be separated from the
supply and return fans which I didn't find how.
Am I missing something here?
Your help is appreciated.
Thank you.
Crina Bosch
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110124/8b842dae/attachment-0001.htm>
More information about the Equest-users
mailing list