[Equest-users] Crankcase heating in Appendix G
Bishop, Bill
wbishop at pathfinder-ea.com
Tue Jan 4 08:20:46 PST 2011
Jacob,
Personally, I think the crankcase heating should be allowed in both the
proposed and baseline models if it is required for that system type in
your region. That is how I have been modeling it. As a compromise, you
could determine the annual crankcase energy by modeling the proposed
with and without it, then take it out of all proposed and baseline
systems and add the same amount as an identical process load in both the
proposed and baseline models.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com www.pathfinder-ea.com
<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of jacob
goodman
Sent: Tuesday, January 04, 2011 11:01 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Crankcase heating in Appendix G
I am working on a reply to some LEED reviewer questions regarding crank
case heating for a PSZ-AC system type for a LEED building. The project
is registered under 90.1 - 2004. The eQuest system type "Packages single
zone" defaults to 0.5 kW of crank case heating which I left in both
models since my proposed model uses the same type system and crankcase
in necessary in the northwest.
The reviewer commented that "because Appendix G does not explicitly
address crankcase heating, it should not be modeled in the baseline
case". This seems to imply that if it is included in the installed units
it need to be in the proposed model, but I need to remove it from the
baseline causing an unfair energy difference.
I didn't find any CIR's, but does anyone have any suggestions?
--
Jacob Goodman , LEED AP, Green Building Specialist
v:509.280.7051 i:www.lseng.com <http://www.lseng.com>
L&S Engineering Associates, Inc.
'High Performance Design'
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/de6f007b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/de6f007b/attachment-0002.jpeg>
More information about the Equest-users
mailing list