[Equest-users] ETTV Value
Ery Djunaedy
ery.mailinglist at gmail.com
Sat Jan 15 05:36:45 PST 2011
Zahid,
First of all, Singapore's building authority may or may not accept the
ETTV calculation based on eQuest simulation. You can always try to make
the case. Arup has made this case at least once that I know of.
To do it in eQuest is quite simple. You simply need to disaggregate the
heat flow through the facade into (1) wall conduction (2) glass
conduction and (3) solar radiation. I think these values are reported in
the standard report (LS-C).
An example can be found here:
Clarice Fong, Wu Xuchao, Ery Djunaedy, "Formulating an Alternative
Methodology for Singapore's Envelope Thermal Transfer Value Calculation:
Accounting for Non-Conventional Shading Strategies", PLEA 2009.
http://www.plea2009.arc.ulaval.ca/Papers/2.STRATEGIES/2.2%20Heating%20and%20Cooling/ORAL/2-2-11-PLEA2009Quebec.pdf
Local resource in Singapore, you can ask Clarice or Xuchao, or you can
always try Prof Chou of NUS.
Hope this helps,
Ery
On 01/15/2011 05:05 AM, m zahid wrote:
> Hi
>
>
> how can i calculate the ETTV (Envelop Thermal Transfer value ) value
> from eQUEST
>
> thanks
>
> zahid
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110115/f6e117a7/attachment-0002.htm>
More information about the Equest-users
mailing list