[Equest-users] HVAC Loads output question
Morrison, Andrew
amorrison at haleyaldrich.com
Thu Jan 27 14:06:37 PST 2011
Is there any way to find loads based on the setpoint temperature, not on the design temperature?
Or - if I made the design temperature equal to the setpoint temperature, would the loads change correspondingly?
From: Brian Gregory [mailto:bgregory at dynamix-ltd.com]
Sent: Thursday, January 27, 2011 4:59 PM
To: Morrison, Andrew
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] HVAC Loads output question
It is my understanding that the loads are calculated based on the "Indoor Design Temperature" and not the setpoint temperature. You can generate hourly reports using the "Space" blocks in the hourly report blocks however you would need to make a separate block for each space.
On Thu, Jan 27, 2011 at 4:47 PM, Morrison, Andrew <amorrison at haleyaldrich.com<mailto:amorrison at haleyaldrich.com>> wrote:
Brian,
Thanks for that input. I have a follow-up question: I looked at the LS-B report and it has a note that says "The above loads are calculated assuming a constant indoor space temperature." Is this temperature equal to the setpoint temperature of the space?
Also, is there a counterpart to this report that outputs hourly values?
Thanks
Drew
From: Brian Gregory [mailto:bgregory at dynamix-ltd.com<mailto:bgregory at dynamix-ltd.com>]
Sent: Thursday, January 27, 2011 4:24 PM
To: Morrison, Andrew
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] HVAC Loads output question
Drew,
I typically use the "LS-B Peak Load Components" report from the sim-output file for loads.
On Thu, Jan 27, 2011 at 1:34 PM, Morrison, Andrew <amorrison at haleyaldrich.com<mailto:amorrison at haleyaldrich.com>> wrote:
Hi,
I'm modeling a 1940s-era apartment building for a geothermal retrofit. The current heating system consists of hot-water radiators supplied by gas-fired boilers. Cooling is supplied by window air conditioning units in each apartment. The ultimate objective is to generate building space heating and cooling loads to size a heat pump and ground heat exchanger - by space heating and cooling loads, I mean the total heat which has to be added or removed by the HVAC system to maintain all conditioned spaces at their set points.
Currently I'm generating hourly loads from the Building HVAC hourly report block using variables 1 & 2, entitled "Building cool load (coils + losses&gains)" and "Building heat load (coils + losses&gains)". Are these the right variables to use, or do I need to look somewhere else?
Thanks,
Drew Morrison
Engineer
Haley & Aldrich, Inc.
8899 Gander Creek Drive
Miamisburg, OH 45342-5432
Office: 937.530.1431
Cell: 937.307.2223
amorrison at haleyaldrich.com<http://amorrison@haleyaldrich.com>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Dynamix
Engineering Ltd
Brian Gregory
Mechanical Engineer
855 Grandview Ave., 3rd Floor Columbus, OH 43215
614-443-1178 ext. 278 www.dynamix-ltd.com<http://www.dynamix-ltd.com/>
--
Dynamix
Engineering Ltd
Brian Gregory
Mechanical Engineer
855 Grandview Ave., 3rd Floor Columbus, OH 43215
614-443-1178 ext. 278 www.dynamix-ltd.com<http://www.dynamix-ltd.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110127/87c97655/attachment-0002.htm>
More information about the Equest-users
mailing list