[Equest-users] Unable to assign a VAV "terminal type"

Carol Gardner cmg750 at gmail.com
Mon Jul 4 09:40:28 PDT 2011


What are you calling your system type? It will have to be VAVS, PVAVS or
PVVT to be able to include VAV boxes.

Carol

On Mon, Jul 4, 2011 at 9:12 AM, Rob S. Young <youngrs at kjww.com> wrote:

> I am working on a model for a project where multi-zone air handling systems
> are being converted to single-duct VAV systems.  I have already completed
> the system changes so that all of the air handling units are single-duct
> VAV.  However, I am unable to change the zones to include VAV boxes.  Under
> each zone in the "Air Flow" tab, the "Zone Terminal and Fans" section is all
> grayed out and will not allow any changes.  I tried deleting the zone and
> re-creating it, but I still have the same issue.  Any advice is much
> appreciated!
>
> Rob
>
> This message and any attachments contain information intended for a
> specific party and may include sensitive or confidential material. If you
> are not the intended recipient, please do not read, copy, use, or disclose
> to others.  Please notify the sender of the delivery error by reply and then
> permanently delete this message and all attachments.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>



-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110704/278f9831/attachment-0002.htm>


More information about the Equest-users mailing list