[Equest-users] Chiller Curves
Rob Hudson
rdh4176 at gmail.com
Wed Jul 20 04:23:19 PDT 2011
I have a new Chiller Curve question/situation. I have created a custom
chiller curve for the EIR = f(PLR) as a cubic function using the following
data inputs:
1 .3313
.75 .2437
.5 .2201
.25 .1928
>From my understanding, the chiller curve seems correct. However, when i
create a hourly report summary for the Corrected Chiller EIR and compare it
to the default EIR equation for this entry, i get 0.034 for the default and
0.072 for my curve at 25% ratio. Why is it that the default is better than
my curve? I have looked at the equation for the default entry and got the
following equations:
EIR = a + b x = c x^2
a = .04812248
b = .69573420
c = .23493889
at 25% this equation results in 0.2367, and my equation gets 0.1928
Is there any other calculations going on in the background that is causing
some problems? I have attached an excel snapshot of the different EIR and
the corrected EIR values for two different chillers in my program. Neither
is currently using the default EIR = f(PLR) curves, they are using custom
curves.
Thanks in advance,
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110720/75a51b8a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: excel snap.bmp
Type: image/bmp
Size: 4500102 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110720/75a51b8a/attachment-0002.bin>
More information about the Equest-users
mailing list