[Equest-users] Create Floor and Space in Detailed Mode
Nick Caton
ncaton at smithboucher.com
Fri Jul 22 11:20:59 PDT 2011
Hi DE!
Sounds like you found the specific solution in this case, but it would
probably help to better understand how to evaluate the problem for the
future:
"Standard writing file errors" are something you'll generally encounter
on trying to either run a simulation (calculate) or open the file.
That's the program generically telling you something is off in BDL...
and this is commonly either a missing input or missing association (easy
occurrence when creating a dummy zone or otherwise deleting/creating
things in detailed mode)... For example: Have you created a zone for
the dummy space and assigned it to the single dummy space? Not doing so
will result in (1) standard writing error.
The phrase "standard writing file error" is of course itself not
intuitive or particularly helpful. Errors are hard to evaluate without
having the files on-hand, which is why others will sometimes ask you to
upload... but better to teach a man to fish!
To investigate most errors that prevent a simulation from completing:
open the project directory, then locate and open your .BDL file in
notepad or another text editor. Ctrl+F to find the word "ERROR" and you
will identify where in your file the error occurred (usually a strong
clue in and of itself), and often a textual description of what was
expected and missing or similar clues to give a better sense of the
problem to be resolved.
The button that looks like a little building with a checkmark up next
to the yellow calculator may be a more user-friendly means of exploring
your BDL errors as you run into them as well, but I tend to forget it's
there and only use it when it occasionally pops up on its own. With
that dialog you can sometimes be "navigated" to where the problem must
be fixed in the eQuest interface.
~Nick
PS: The first popup warning you saw on creating a floor about default
data is just fluff... fill in the blank fields for width/depth/etc. in
the following prompt and it won't show up again. You may see similar
"cautionary" pop-ups when creating select other items in detailed. I'm
guessing this is just a sign that there isn't any library default entry
for new floor dimensions.
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kelsey
VanTassel
Sent: Friday, July 22, 2011 9:18 AM
To: DongEun Kim
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Create Floor and Space in Detailed Mode
Nevermind, I didn't see the message that your issue was resolved. Glad
you figured it out.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com <http://www.sustaineng.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kelsey
VanTassel
Sent: Friday, July 22, 2011 9:15 AM
To: DongEun Kim
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Create Floor and Space in Detailed Mode
If you want to attach the .inp and .pd2 files, I will take a quick look
at them.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com <http://www.sustaineng.com/>
From: DongEun Kim [mailto:equested at gmail.com]
Sent: Thursday, July 21, 2011 7:28 PM
To: Kelsey VanTassel
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Create Floor and Space in Detailed Mode
Kelsey,
The thing is, I 've tried that too. I still got the "standard file
writing errors" when I hit the run button.
That did not happen to anyone?
Thank you.
2011/7/21 Kelsey VanTassel <KVanTassel at sustaineng.com>
You do not need to create a new floor. Just create the new space as a
child of one of the existing floors.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com <http://www.sustaineng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of DongEun Kim
Sent: Thursday, July 21, 2011 3:35 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Create Floor and Space in Detailed Mode
HI all!
I really need your help here.
I 've been trying to create Dummy zone for my DOAS system in Detailed
Mode.
First, I create "Floor" then its child "Space" whose area is same as the
zone served by the DOAS. I used 'Box' method.
However, an error massage that says "Unable to locate default data for
Command=FLOOR,Type=0, Keyword=WIDTH" keeps popting up, followed by
"standard file writing errors. "
How can I fix this problem?
Thank you in advance!
~DE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110722/7f620902/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110722/7f620902/attachment-0002.jpeg>
More information about the Equest-users
mailing list