[Equest-users] insufficient heating capability
DongEun Kim
equested at gmail.com
Mon Jul 25 04:12:44 PDT 2011
Thank you Carol!
I modified "Min Design Flow(cfm/ft2) .
However, "insufficient heating" warning is keep showing.
Only thing seems to work to solve this problem is to increase heating
capacity is Reheat delta T.
(Its system is VAV with Reheat).
What I can't understand the most is that specifying heating capacity of main
heating coil doesn't
affect the heating capacity anyhow.
Any thoughts on this anyone???
Thank you!
DE
2011/7/25 Carol Gardner <cmg750 at gmail.com>
> Hi DE,
>
> If you look around at all the defaults you will probably find that
> somewhere eQUEST is defaulting to 0.5 cfm/sf for your supply air. This is
> often insufficient to meet your heating/cooling requirements. Things I have
> done in the past to fix this is to use the same cfm/sf as the proposed
> building uses, or look in the little ASHRAE Pocket Guide for what they
> recommend for your building type. These two numbers will likely be similar
>
> Carol.
>
> On Sun, Jul 24, 2011 at 5:16 PM, DongEun Kim <equested at gmail.com> wrote:
>
>> Thank you John,
>>
>> But isn't airflow supposed to be auto-sized if not specified?
>>
>> I intentionally leave the flowrate blank to let the program calculate the
>> cfm that serves load the best.
>>
>> Should still I specifiy cfm?
>>
>> DE
>>
>> 2011/7/23 John Aulbach <jra_sac at yahoo.com>
>>
>>> Try increasing airflow.
>>>
>>> *From:* DongEun Kim <equested at gmail.com>
>>> *To:* equest-users at lists.onebuilding.org
>>> *Sent:* Friday, July 22, 2011 12:13 AM
>>> *Subject:* [Equest-users] insufficient heating capability
>>>
>>> Hi eQuesters!
>>>
>>> Can anyone help me here?
>>>
>>> I installed main heating coil as well as reheat coil with delta T=30.
>>>
>>> Heating capacity and cfm is not defined so that they will be auto-sized.
>>>
>>> And, I keep having this warning saying that the system "might have
>>> insufficient heating capability."
>>>
>>> I increased "Zone Entering Max Supply Temp", "Hot Deck Max Leaving
>>> Temp." But, the problem stays.
>>>
>>>
>>> How do I increase the heating capability?
>>> Thank you !!
>>>
>>> DE
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
> Carol Gardner PE
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110725/f22956e4/attachment-0002.htm>
More information about the Equest-users
mailing list