On Tue, Jul 26, 2011 at 7:28 AM, Bruce Easterbrook <bruce5 at bellnet.ca>wrote:
> The intent of 90.1 and using a modelling program like eQuest is to
> size the equipment closer to the actual demand. The 15% and 25% variance
> factors were used in the past before the computerized modelling we are using
> today. Doing load calculations buy hand or using a spreadsheet made for
> much more deviation between the calculations and the building. Less things
> were accounted for as well. By providing more certainty using a modelling
> program we should be reducing these safety factors. These factors are still
> a best guess and the designer must keep all this in mind. The next step in
> the process is specifying the equipment for the building. So if the
> modeller has a 15% SF on the equipment and because most equipment is built
> with discrete sizes, the specifier adds another 20% by picking the next size
> up you can see how things start to chain together and get out of control.
> Next step is bidding, the specifier uses Trane as base bid but Carrier wins
> the process and submits shop drawings. They are normally required to
> provide a superior bid, there is another 8%. Remember as well the second
> and third increases are now compounding, we are not 43% over sized but
> probably more like 50%+. My point is the original design and SF should be
> used from start to finish.
> Next question is where to apply these factors. They should be on the
> air handlers. If your fan is too small and your coils are too small what
> you get supplied from the plant is irrelevant. You physically do not have
> the equipment to handle the diversity. So the method is to account for the
> diversity in the end units, and have the plant at 1.0 or less. Your SF on
> the units flows through to the plant. Note I mentioned "or less". Consider
> a building with a north south split. An AHU on the north side will only see
> diversity due to weather. A south side AHU will see diversity due to
> weather and sun. You may consider different diversity factors for each.
> Throw in 10 buildings of different sizes and orientations you can see the
> effect in the deviation on the plant using old methods. eQuest due to the
> through nature of the model can account for all this. Can is a critical
> word, it all depends on the model. There is still diversity in the model.
> The amount depends on what the money people want to spend modelling. LEED
> is the attempt to control these factors, to set a minimum quality level for
> the model. It is now realized this is not enough. Original LEED buildings
> on the majority do not perform as the model suggested they would. Now
> commissioning is the new buzz word. As if that is the only reason. If your
> units are too small commissioning won't fix the problem either. If your
> units are too big the system will work but not efficiently. Part of the
> problem is the process, hence the proposal that modellers be PE's. That may
> help but it wouldn't solve many of the problems. The model is important but
> is only effective if used as a reference start to finish. The safety
> factors come from using eQuest and doing project reviews. Comparing the
> actual building performance to the model and taking a look at the allowances
> for variance. There is only one group responsible for this whole process,
> it is the mechanical engineer who has assumed responsibility for the
> building project.
> The short answer is there is no rule of thumb for the safety factors.
> More experience allows you to guess better but it is still a guess because
> every project is different. Model feedback is spotty. The safety factors
> should be applied at the terminal equipment not at the plant. Mostly, 15%
> for cooling and 25% for heating are too big. In most cases .5 cfm/SF is too
> small. But that is where I start. Get the model built and running, let it
> run on defaults, let it determine the initial sizing, thoroughly review the
> sim output, then start tuning it.
> Bruce Easterbrook P.Eng.
> Abode Engineering
>
> On 25/07/2011 07:47 PM, Arunabha Sau wrote:
>
> Howdy!
>
>
> So, I just saw a project which has applied its oversizing factors (1.15
> for cooling and 1.25 for heating) to the plant rather than the air handlers.
> ASHRAE 90.1 Appendix G page 180, G3.1.2.2 Equipment capacities does not
> specify where the oversizing should occur. Have you seen this method used
> before? Is it an acceptable and accurate way of meeting the baseline
> modeling requirements?
>
> I appreciate your help.
>
>
>
>
> Much thanks,
> Aru
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110726/a6c012c9/attachment-0002.htm>
More information about the Equest-users
mailing list