[Equest-users] cooling/heating schedule
Charles Land
cland at geo-marine.com
Thu Jun 9 08:24:45 PDT 2011
Your cooling and heating schedules will still have to be temperature schedules for a two-pipe system. To make your 2-pipe system switch from heating to cooling you want to go under your 2-pipe loop and specify a “snap” temperature. This is found under the operations tab, “loop operation”.
You can also create an “on/off/temp” schedule under the availability schedules of your unit’s cooling and heating coils if there are additional periods when cooling or heating are not allowed for specific air handling units.
I hope this answers your question.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of ???
Sent: Thursday, June 09, 2011 11:02 AM
To: equest-users
Subject: [Equest-users] cooling/heating schedule
why I can not creat cooling/heating schedule using schedule type" on/of/tem" when I mode a FC with 2-pipe loop?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110609/54932b0d/attachment-0002.htm>
More information about the Equest-users
mailing list