[Equest-users] LEED Review Comment - Exhaust Fans
Paul Diglio
paul.diglio at sbcglobal.net
Fri Jun 17 14:11:41 PDT 2011
Kelsey:
I do not understand why you do not expect the GBCI reviewer to be competence in
the software used to simulate a particular building. Your comment does not make
sense.
It is the same as saying the modeler does not have to be competent in the
software he or she uses to simulate the building. Get real, there is a minimum
level of competency required for both the simulator or reviewer on any project.
Paul Diglio
________________________________
From: Kelsey VanTassel <KVanTassel at sustaineng.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; Nathan Miller
<nathanm at rushingco.com>; Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
Cc: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Fri, June 17, 2011 5:04:39 PM
Subject: RE: [Equest-users] LEED Review Comment - Exhaust Fans
Why should LEED reviewers be expected to be experts in every type of modeling
software? The software itself is just a calculator. As long as it meets the
requirements, it shouldn’t matter which program was used. The LEED reviewers
judge the models on the results and the quality of the inputs. Garbage In,
Garbage Out.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Friday, June 17, 2011 3:55 PM
To: Nathan Miller; Pasha Korber-Gonzalez
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED Review Comment - Exhaust Fans
Nathan:
I am being fair and I expect the reviewers to experts in every energy modeling
program that is allow under Appendix G. The GBCI should refer specific projects
using eQuest or Trace or HAP to reviewers that are competent in that software.
Paul Diglio
________________________________
From:Nathan Miller <nathanm at rushingco.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; Pasha Korber-Gonzalez
<pasha.pkconsulting at gmail.com>
Cc: equest-users at lists.onebuilding.org
Sent: Fri, June 17, 2011 4:45:45 PM
Subject: RE: [Equest-users] LEED Review Comment - Exhaust Fans
Paul,
I think you are being a bit unfair to the reviewers (full disclosure, I reviewed
EAc1 submittals in the pre-GBCI days, when consulting teams performed the
reviews).
They don’t go into a review with all of the knowledge that we had while building
up the model. All they get is the template and the supplementary documentation
that we as submitters have decided to provide them. Sometimes these documents
are a bare minimum, and sometimes it is a flood of information that is too much
to try to go over.
They have to piece together if the saving you are presenting make sense given
the building and system components that have been described. It can be quite a
puzzle to figure out , for example, if it makes sense that someone is showing
35% ventilation fan energy savings when comparing their series VAV system to the
baseline parallel VAV system. Reviewers can try to be helpful, and point out
specific items they want verified, though sometimes they do in fact make
mistakes and look like idiots for what they are asking (I’m thinking of the
electric resistance heating question from earlier in the thread). Alternately
they can be vague with their comments and put the onus on the submitter to prove
that the savings make sense, but that can be equally frustrating to respond to.
Additionally I don’t think it is fair for them to be experts in every energy
modeling program that is allowed under Appendix G. That is completely
unrealistic. They won’t necessarily know that one program puts boiler
supplementary energy in the space heating end use category, as that could be
different with different programs, and certainly isn’t intuitive.
Sincerely,
Nathan Miller, PE, LEED®AP
Senior Energy Engineer/Mechanical Engineer
D206-788-4577
www.rushingco.com
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Friday, June 17, 2011 1:03 PM
To: Pasha Korber-Gonzalez
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED Review Comment - Exhaust Fans
Pasha:
No problem, it is raping as far as I am concerned. GBCI is using incompetent
reviewers and they expect us to train them. They take the application fees and
offer nothing in return except ridiculous comments.
I have a similar problem with Northeast Utilities serving CT and MA. NU offers
a modeling incentive of $6,000, an efficiency incentive up to $2.00 ft2 and a
LEED incentive up to $15,000. They employ reviewers that have no modeling or
eQuest experience. One reviewer expected that I would explain how custom
performance curves are built for an eQuest VRV system.
I told them I wasn't in the business of training their employees at the client's
expense. I would provide the manufacturer's performance tables and my eQuest
curve coefficients, but I was not going to spend time to explain how to verify
that my curves are accurate. They need to spend money to train their reviewers
or hire experienced reviewers.
I feel that the comments that you received from the GBCI were indicative of a
person who has no clue and is not qualified to review building simulations.
Regards,
Paul Diglio
________________________________
From:Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Cc: equest-users at lists.onebuilding.org
Sent: Fri, June 17, 2011 3:45:23 PM
Subject: Re: [Equest-users] LEED Review Comment - Exhaust Fans
Hi Paul-- thanks for receiving my comment in the most professional sense of the
term as it relates to the economics of the LEED simulation & Compliance
markets.
I didn't really feel it was unprofessional, but I didn't desire to offend anyone
with the terms that i chose. I was pretty sure that I wasn't completely alone
with the 'feeling' or sense I was getting from others comments I've seen with
the forum (past & present).
I offer a sincere professional apology if my chosen adjectives offended anyone.
(were they adjectives? I don't know I'm not an english major...) :)
Cheers,
Pasha
On Fri, Jun 17, 2011 at 1:41 PM, Paul Diglio <paul.diglio at sbcglobal.net> wrote:
Pasha:
I agree with your 'raping' verb and do not think it is inappropriate for the
forum. Dan is out of sync.
Paul Diglio
________________________________
From:Daniel Knapp <danielk at arborus.ca>
To: Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
Cc: equest-users at lists.onebuilding.org
Sent: Fri, June 17, 2011 3:32:24 PM
Subject: Re: [Equest-users] LEED Review Comment - Exhaust Fans
Dear Pasha,
client has already paid them. DEAR USGBC---please stop raping the industry for
the money monopoly that you have created. The sense of GREED is oozing from
everything that comes out of USGBC/GBCI with a price tag on it or a cost
associated with it.
I hear that you are very frustrated with the review process, however, I find
this kind of language inappropriate for a public forum and would ask that you
take more care in the future.
With all best wishes,
Dan
—
Daniel Knapp, PhD, LEED® AP O+M
danielk at arborus.ca
Arborus Consulting
Energy Strategies for the Built Environment
www.arborus.ca
76 Chamberlain Avenue
Ottawa, ON, K1S 1V9
Phone: (613) 234-7178 ext. 113
Fax: (613) 234-0740
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110617/2c369913/attachment-0002.htm>
More information about the Equest-users
mailing list