Regarding DCV there are a few things to know:
1. demand is based on the number of people in the space and the outdoor air
per person specified at the zone level. If your outdoor air rate is not
entered as a per person air rate, then DCV will not work properly
2. If your fans are not constant volume, ie they can cycle or they are
variable speed, then you need to make sure that the proper ventilation air
is supplied in your base case. Usually, I set the fan flow to 'variable'.
If, in reality, the fans cycle on and off, I change the fan curve to
linear. Then, i set the minimum flow to be equal to the outdoor air rate
fraction. Otherwise, implementing DCV can actually RAISE energy.
On Wed, Mar 9, 2011 at 10:59 AM, <MatthewRLarson at eaton.com> wrote:
> Charles,
>
>
>
> Regarding the DCV, you need to specify the “Minimum OA Control Method”
> under the Outdoor Air tab for the system to state whether the CO2 sensor is
> in the return or in the space. Then at the zone level, specify the “Minimum
> Flow Control” under the Air Flow tab to state if the minimum OA resets up or
> down depending on occupancy level. To ensure the amount of OA going into a
> space doesn’t go below the ASHRAE 62.1 minimum, I always input the OA Flow
> per Person and/or Flow per Area at the zone level as well. DCV has always
> been something I’ve been a little dicey about so any additional
> suggestions/comments would be great.
>
>
>
> Thanks,
>
>
>
> *Matthew Larson, LEED AP BD+C
> *Project Engineer
>
> Energy Solutions Group
>
> E M C Engineers, Inc.
> Eaton’s Electrical Services & Systems
> 143 Union Blvd, Suite 350
> Lakewood, CO 80228
> tel: +1 303 328-3419
> mobile: +1 303 668-2511
> fax: +1 303 974-1239
>
> MatthewRLarson at Eaton.com
> www.eaton.com/energysolutions
>
> [image: image001]
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Greg Collins
> *Sent:* Tuesday, March 08, 2011 5:53 PM
> *To:* Charles Welch; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] EMS Control System Modeling
>
>
>
> Charles - A quick suggestion for the setback is to try setting your system
> fans to "cycle on any." Otherwise, your system might not kick on to
> maintain setback temperatures.
>
>
>
> *Greg Collins*
> GLUMAC | (949) 833-8190
>
>
>
> *From:* Charles Welch [mailto:cwelch at capitalreviewgroup.com]
> *Sent:* Tuesday, March 08, 2011 4:24 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] EMS Control System Modeling
>
>
>
> I am doing an quick estimate for adding EMS control to an existing HVAC
> system (schools) which incorporate the following measures
>
>
>
> 1) Automatic thermostat setbacks for building occupation
>
> 2) Demand controlled ventilation
>
> 3) Economizers
>
>
>
> Here are my "challenges"
> 1) Simulation with setback temperatures shows no reduction in energy
>
> 2) I am unsure how to handle DCV
>
> 3) Simulation with economizers show very little reduction
>
>
>
> I would appreciate any pointers, suggestions, etc. on what to do here.
>
> I would especially appreciate any example files to see how you input the
> data to get proper results.
>
>
>
>
>
> Thanks in advance for any help.
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110309/90ed081e/attachment-0001.htm>
More information about the Equest-users
mailing list