Hi there Xiaoyang,
VAV min flows can be set both in wizards and in detailed edit modes.
See following screenshots.
The "standard" depends on the HVAC design, and specifically how
ventilation air is being distributed. There's a range of CFM's that the
factory will set as a minimum terminal unit at depending on the size,
but it may well be zero if you are distributing ventilation air via DOAS
in certain ways. I'd suggest asking your HVAC designer directly what
the minimum is for each unit (it's probably scheduled), and use that
info to either come up with an average for each zone or to set the
minimum for each zone separately.
Here's the wizard...
... and in detailed, double click on a space served by a VAV system,
under the Airside HVAC tab, to find the following window. In this case,
the minimum flow is set to 30% (0.30):
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
xiaoyang shi
Sent: Friday, March 11, 2011 2:35 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VAV minimum flow
Hi folks,
Do you know how to set the "VAV minimum flow" (percentage) at the "HVAC
zones: temperatures and Air Flows" panel? eQUEST default number is 40%.
Is there any standard?
Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20535 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21659 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment-0003.png>
More information about the Equest-users
mailing list