[Equest-users] ASHRAE 62.1 Unoccupied Vnetilation
    Nick Caton 
    ncaton at smithboucher.com
       
    Mon Mar 14 09:57:36 PDT 2011
    
    
  
In agreement and in extension of Jeremy/Paul’s thoughts:
 
62.1-2007 and 2004 define a “breathing zone” as “the region in an occupied space…” in the glossary.   
 
Once a space is unoccupied, it ceases to have a breathing zone.  When there’s no breathing zone, per 6.2.6.1, there’s little to discuss ;).
 
Do provide ventilation for off-gassing.  Another good example from my short experience has been tire storage.
 
~Nick
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Monday, March 14, 2011 8:19 AM
To: Jeremy Poling; Charles Welch; equest-users at lists.onebuilding.org
Subject: [Equest-users] ASHRAE 62.1 Unoccupied Vnetilation
 
Jeremy:
I don't see anything in 62.1 that implies ventilation is required during the unoccupied mode.
I agree that there are off-gassing considerations to be taken into account.  62.1-2004 had a section that stated, in so many words, that if there was an accumulation of contaminants during the unoccupied period, the fans shall be started before occupancy to purge the contaminants.  I did not see this in 62.1-2007, but I do not have a searchable copy, just a cut & paste from Real-Read.
Some designers specify a night purge mode to clear the air after the cleaning crew has left the building in order to purge the air of the cleaning solution odors.
62.1-2007, section 6.2.6.1 states that the "Ventilation systems shall be designed to be capable of providing the required ventilation rates in the breathing zone whenever the zones served by the system are occupied".  I take the "required ventilation rates" to mean those defined in Table 6.1 which is where the CFM per person and the CFM/Ft2 is defined.
I would be interested if anyone else on the forum shares your interpretation.
Paul Diglio
 
 
________________________________
From: Jeremy Poling <Jeremy.Poling at transwestern.net>
To: Paul Diglio <paul.diglio at sbcglobal.net>; Charles Welch <cwelch at capitalreviewgroup.com>; equest-users at lists.onebuilding.org
Sent: Mon, March 14, 2011 12:40:06 AM
Subject: RE: [Equest-users] EMS Control System Modeling
Paul,
 
I just have a literal viewpoint – I think it is more me identifying a problem with equivalence in the codes: 90.1 allows cycling of fans during unoccupied hours but I haven’t seen anything in 62.1 that says you can turn off the area-based component of the ventilation calculation.  I’m in the position most of the time of either modeling someone else’s design or reviewing a model built by someone else so this usually becomes a discussion I have if the model is attempting to take credit for DCV strategies.  I mean, it is very literal, but the basic VRP equation is Ra*Az + Rp*Pz=Vbz and the only thing that changes over the short-term is Pz, right?  The 62.1-2007 User’s Manual on page A-6 points to Section 5.4 and Section 6.2.6.1 that state that ventilation is required whenever zones are occupied.  That said, on page 6-2 the User’s Manual describes the two components of the VRP the way I mentioned earlier: one for the “occupant-related component” and the other for the “building area-based component” that is described as “The building area-based component is intended to dilute sensory contaminants emitting from materials and furnishings within the space, and from non-occupant activities and processes taking place within the space.”  From my reading, this agrees that there are sources of IAQ contamination that originate from the building itself that have nothing to do with the occupancy of the building.  Since the building is present 24/7 it would make sense that it is generating IAQ contaminants 24/7 and therefore, those contaminants need dilution over that time.  So the math says the answer to the equation cannot be 0, but in reality this will represent an energy penalty in most climate zones for a large portion of the year.
 
Thoughts?  I’m definitely okay being proven wrong here, but I haven’t found anything in the text of the standard that overtly confirms that no outdoor airflow should be provided during unoccupied times.
 
Jeremy R. Poling, PE, LEED AP+BDC
 
 
From: Paul Diglio [mailto:paul.diglio at sbcglobal.net] 
Sent: Friday, March 11, 2011 7:13 PM
To: Jeremy Poling; Charles Welch; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EMS Control System Modeling
 
Jeremy:
Are you saying that one needs to provide the Az amount of ventilation air during unoccupied hours?  So you model the fans to run 24 X 7 to provide ventilation?
Paul Diglio
 
________________________________
From: Jeremy Poling <Jeremy.Poling at transwestern.net>
To: Charles Welch <cwelch at capitalreviewgroup.com>; equest-users at lists.onebuilding.org
Sent: Fri, March 11, 2011 3:03:34 PM
Subject: Re: [Equest-users] EMS Control System Modeling
Charles,
 
One more thought for your consideration: since the DCV is based on occupancy, the occupancy schedule is also going to drive it in reality and in the model (as you’re aware – just stating for the record).  Because of that, the hourly people-schedule is going to drive the results given by the model.  It may make sense to go through and look at that schedule in detail to be certain it reflects your best understanding of how the spaces will be occupied.  Following on that thought, a very real example of where DCV can save energy is going to be after hours or during non-peak occupancy times (for the large conference room spaces, etc.).  ASHRAE 62.1-2007 Section 6.2.6 and Section 6.2.7 both will tell you how low your minimum ventilation rate can go during the unoccupied period.
 
A note for everyone who reads this: I’ve been told I take a very literal read of the code so this may not agree with your understanding of it, but in my literal view I see Section 6.2.7 allowing you to reduce the value of Pz in your VRP calculations to 0 during unoccupied times but since Az remains fixed you are not allowed to reduce the outdoor air down to 0 during unoccupied times.  Explanatory material behind the development of the current procedures in the standard explains that the VRP calculation has two components: one to deal with IAQ associated with people-generated contaminants and one for building-generated contaminants.  Regardless of your view on that, you should be able to arrive at a minimum OA number that is LESS than the amount specified using peak occupancy or time-averaged occupancy (per 6.2.6).
 
So – in summary: I would double check your occupancy schedule to make sure it reflects what you are expecting to see in the building and then double check your minimum OA setting to make sure it will allow the system to reduce OA when occupancy drops.  Also, one possible “exaggeration” may be viewing it from a system energy perspective or a whole building perspective: if I leave one zone and go to another and both zones have DCV, then the one I left will reduce OA and the one I entered will increase OA but the net effect should be to balance each other out (oversimplified, but the concept is what I was going for not the math).  So when you look at building-level energy consumption for the ventilation system the individual unit savings will wash out.  The only savings you’ll see are when people leave the building altogether.
 
Jeremy R. Poling, PE, LEED AP+BDC
Manager | Sustainability Services
TRANSWESTERN
234 W. Florida St.
Milwaukee, WI  53204
Phone 414.255.3322 | Fax 414.224.7780 | Mobile 414.426.7273
Jeremy.Poling at Transwestern.net
http://www.transwestern.net/Energy-Sustainability.asp
 
 
 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Charles Welch
Sent: Friday, March 11, 2011 1:14 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EMS Control System Modeling
 
Thank you very much to those who helped me out with this... Finally made some good headway.
 
Quick question....
 
Modeling the DCV for my location (AZ) I shows only a very small improvement in energy consumption for my HVAC, does this sound correct?
I have always been "led to believe" by the local control companies that DCV is a huge improvement?
Myth, sales "exaggeration", or have some of them found a way to control the DCV in a manner that I am not modeling correctly? 
Opinions or pointers appreciated.
 
----- Original Message ----- 
	From: Karen Walkerman <mailto:kwalkerman at gmail.com>  
	To: MatthewRLarson at eaton.com 
	Cc: GCollins at glumac.com ; cwelch at capitalreviewgroup.com ; equest-users at lists.onebuilding.org 
	Sent: Wednesday, March 09, 2011 2:48 PM
	Subject: Re: [Equest-users] EMS Control System Modeling
	 
	Regarding DCV there are a few things to know:
	 
	1.  demand is based on the number of people in the space and the outdoor air per person specified at the zone level.  If your outdoor air rate is not entered as a per person air rate, then DCV will not work properly
	 
	2.  If your fans are not constant volume, ie they can cycle or they are variable speed, then you need to make sure that the proper ventilation air is supplied in your base case.  Usually, I set the fan flow to 'variable'.  If, in reality, the fans cycle on and off, I change the fan curve to linear.  Then, i set the minimum flow to be equal to the outdoor air rate fraction.  Otherwise, implementing DCV can actually RAISE energy.
	 
	On Wed, Mar 9, 2011 at 10:59 AM, <MatthewRLarson at eaton.com> wrote:
	Charles,
	 
	Regarding the DCV, you need to specify the “Minimum OA Control Method” under the Outdoor Air tab for the system to state whether the CO2 sensor is in the return or in the space.  Then at the zone level, specify the “Minimum Flow Control” under the Air Flow tab to state if the minimum OA resets up or down depending on occupancy level.  To ensure the amount of OA going into a space doesn’t go below the ASHRAE 62.1 minimum, I always input the OA Flow per Person and/or Flow per Area at the zone level as well.  DCV has always been something I’ve been a little dicey about so any additional suggestions/comments would be great.
	 
	Thanks,
	 
	Matthew Larson, LEED AP BD+C
	Project Engineer
	Energy Solutions Group
	E M C Engineers, Inc.
	Eaton’s Electrical Services & Systems 
	143 Union Blvd, Suite 350
	Lakewood, CO 80228
	tel: +1 303 328-3419
	mobile: +1 303 668-2511
	fax: +1 303 974-1239
	MatthewRLarson at Eaton.com 
	www.eaton.com/energysolutions  
	Error! Filename not specified.
	 
	From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg Collins
	Sent: Tuesday, March 08, 2011 5:53 PM
	To: Charles Welch; equest-users at lists.onebuilding.org
	Subject: Re: [Equest-users] EMS Control System Modeling
	 
	Charles - A quick suggestion for the setback is to try setting your system fans to "cycle on any."  Otherwise, your system might not kick on to maintain setback temperatures. 
	 
	Greg Collins
	GLUMAC | (949) 833-8190
	 
	From: Charles Welch [mailto:cwelch at capitalreviewgroup.com] 
	Sent: Tuesday, March 08, 2011 4:24 PM
	To: equest-users at lists.onebuilding.org
	Subject: [Equest-users] EMS Control System Modeling
	 
	I am doing an quick estimate for adding EMS control to an existing HVAC system (schools) which incorporate the following measures
	 
	1)    Automatic thermostat setbacks for building occupation
	2)    Demand controlled ventilation
	3)    Economizers
	 
	Here are my "challenges"
	1)    Simulation with setback temperatures shows no reduction in energy
	2)    I am unsure how to handle DCV
	3)    Simulation with economizers show very little reduction
	 
	I would appreciate any pointers, suggestions, etc. on what to do here.
	I would especially appreciate any example files to see how you input the data to get proper results.
	 
	 
	Thanks in advance for any help.
	  
	 
	
	_______________________________________________
	Equest-users mailing list
	http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
	To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
	 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/22fe1aaf/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/22fe1aaf/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3293 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/22fe1aaf/attachment-0001.gif>
    
    
More information about the Equest-users
mailing list