[Equest-users] Skylight + Plenum
Kelsey VanTassel
KVanTassel at sustaineng.com
Tue Mar 15 17:11:26 PDT 2011
Wizard mode will automatically do both for you, but if you are detailed edit mode here’s how you make a skylight and return air plenum:
Right-click on your space and select “create child component”>”child exterior wall”
Name it something like “skylight roof” and select “create from scratch”
Under “construction” select “library”
Under “starting points” select “Skylt Roof Construction”. Click OK
Under Location select “Top”
In the wall properties window, overwrite the Z value with the height of your roof. The default that is there is the ceiling height. Click OK.
Right-click the new exterior wall you just made and select “create child component”>”child window”
Make your skylight.
In the internal loads tab, right-click your plenum space. Under “zone type”, select “plenum”
Under the air-side HVAC tab, select your system
Under “return air path”, select “plenum”
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com<http://www.sustaineng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rimes, Christie
Sent: Tuesday, March 15, 2011 6:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Skylight + Plenum
Hi,
I am modeling a displacement system therefore need a plenum to model the loads that go straight into the return air plenum. However I also have a skylight in this area require that the lighting pass through to the occupied zone. Any Ideas?
Christie Rimes, LEED BD+C
Designer
WSP ▪ FLACK + KURTZ
405 Howard Street, Suite 500
San Francisco, CA 94105
Direct: 415.402.2727 | Main: 415.398.3833
www.wspfk.com<http://www.wspfk.com/>
Ensuring that today’s built environment preserves the natural environment in which we all live.
We are WSP. United by our difference.
WSP is one of the world’s fastest-growing design, engineering and management consultancies. Specializing in property, transport and environmental projects, we work with clients to create built and natural environments for the future.
CONFIDENTIAL
This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110315/38c364e7/attachment-0001.htm>
More information about the Equest-users
mailing list