[Equest-users] Earth Air Heat Exchanger (EAHX,	EAHE) - simulation results import to eQuest?
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Thu Mar  3 13:30:15 PST 2011
    
    
  
Xiangjin,
 
I have looked at modeling ETAHE for eQUEST and did not come up with a
solution. You could create a custom weather file that uses the earth
tube hourly temperatures as outside air temperatures to model the effect
on the AHU, but then of course you are altering the building envelope
heating/cooling loads.
 
You could try an exceptional calculation method. Using a spreadsheet,
use the difference in temperature between hourly earth tube inlet and
outlet temperatures, and the hourly flow rate, to calculate the energy
added to or removed from the air. Then use the heating/cooling
efficiencies of the AHU to determine the energy saved.
 
Regards,
Bill
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114                F: (585) 325-6005
wbishop at pathfinder-ea.com           www.pathfinder-ea.com
<http://www.pathfinder-ea.com/> 
P   Sustainability - the forest AND the trees. P 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Xiangjin Yang
Sent: Thursday, March 03, 2011 3:37 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Earth Air Heat Exchanger (EAHX, EAHE) -
simulation results import to eQuest?
 
Hello, 
We are under almost the same situation. Did you finally get a solution
of this problem?
We have a project using earth pipe preheating/cooling as renewable
energy application. We got a set of hourly temperature output from
simulation. We would like to input this set of temperature as condition
of a dummy zone. 
Does anyone knows how  to input these data into equest?
Or if there is any other solution on how to include earth pipe outcome
temperature into AHU define in equest? 
Regards,
 
 
Xiangjin Yang Ph.D. 
Junior Mechanical Designer 
 
MCW Consultants Ltd. <http://www.mcw.com> 
156 Front Street West Suite 600 
Toronto, ON M5J 2L6 
Phone 416-598-2920 
Fax 416-598-5394 
 
This e-mail may be privileged and confidential. Any unauthorized use is
strictly prohibited. If you received this e-mail in error, please
contact the sender directly. 
 
P Please consider the environment before printing this e-mail 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110303/f1973186/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110303/f1973186/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list