[Equest-users] Inputting Elevator and Cooking Loads on	Sub-Meters
    James Hansen 
    JHANSEN at ghtltd.com
       
    Fri Mar  4 06:52:24 PST 2011
    
    
  
Assign the sub-meter to EM1.  Otherwise it will give you an error.  Open up the BDL file to troubleshoot errors like this.
-James
On Mar 4, 2011, at 9:24 AM, "Grayson Jordan" <grayson at castrucciarchitect.com> wrote:
> Hi,
> 
>  
> 
> I am attempting to show elevator and cooking loads on sub-meters so that I can demonstrate energy use for each of these loads discreetly.
> 
>  
> 
> I have attempted setting them up as direct loads, with corresponding schedule to the Misc. Loads.
> 
>  
> 
> I have set them up as Sub-Meters and as Building Meters.
> 
>  
> 
> eQuest allows me to set up one sub or building meter no problem.  When I add the second, I get an error and eQuest won’t run the simulation.
> 
>  
> 
> Any idea on how to troubleshoot?
> 
>  
> 