[Equest-users] EMS Control System Modeling
Paul Diglio
paul.diglio at sbcglobal.net
Fri Mar 11 11:33:05 PST 2011
I never heard of DCV implemented with cycling fans. Per 90.1 and our CT State
Code the fan needs to run continuously when the space is occupied. Most codes
require compliance with 90.1 whether we are modeling to that standard or not.
How can you provide the necessary ventilation air if you do not know how long
the fan will run each hour? Do you model the fan to run 3 times per hour and
bring in additional ventilation air so that the hourly average meets 62.1
standards?
My experience is with modeling DCV in both eQuest and using exceptional
calculations via Excel. I have verified the energy savings after the DCV
measure has been installed. You might expect a 6-8% savings in cooling and
heating energy attributed to the air handling units that have implemented this
measure. Often the simple payback is over 5 years because DDC CO2 sensors are
expensive. Of course, it depends on the unit size and the occupancy load.
Paul Diglio
________________________________
From: Charles Welch <cwelch at capitalreviewgroup.com>
To: equest-users at lists.onebuilding.org
Sent: Fri, March 11, 2011 2:14:17 PM
Subject: Re: [Equest-users] EMS Control System Modeling
Thank you very much to those who helped me out with this... Finally made some
good headway.
Quick question....
Modeling the DCV for my location (AZ) I shows only a very small improvement in
energy consumption for my HVAC, does this sound correct?
I have always been "led to believe" by the local control companies that DCV is
a huge improvement?
Myth, sales "exaggeration", or have some of them found a way to control the DCV
in a manner that I am not modeling correctly?
Opinions or pointers appreciated.
----- Original Message -----
From: Karen Walkerman
>To: MatthewRLarson at eaton.com
>Cc: GCollins at glumac.com ; cwelch at capitalreviewgroup.com ;
>equest-users at lists.onebuilding.org
>
>Sent: Wednesday, March 09, 2011 2:48 PM
>Subject: Re: [Equest-users] EMS Control System Modeling
>
>
>Regarding DCV there are a few things to know:
>
>
>
>1. demand is based on the number of people in the space and the outdoor air
>per person specified at the zone level. If your outdoor air rate is not
>entered as a per person air rate, then DCV will not work properly
>
>
>2. If your fans are not constant volume, ie they can cycle or they are
>variable speed, then you need to make sure that the proper ventilation air is
>supplied in your base case. Usually, I set the fan flow to 'variable'. If,
>in reality, the fans cycle on and off, I change the fan curve to linear.
> Then, i set the minimum flow to be equal to the outdoor air rate fraction.
> Otherwise, implementing DCV can actually RAISE energy.
>
>On Wed, Mar 9, 2011 at 10:59 AM, <MatthewRLarson at eaton.com> wrote:
>
>Charles,
>>
>>Regarding the DCV, you need to specify the “Minimum OA Control Method”
>>under the Outdoor Air tab for the system to state whether the CO2 sensor is
>>in the return or in the space. Then at the zone level, specify the
>>“Minimum Flow Control” under the Air Flow tab to state if the minimum OA
>>resets up or down depending on occupancy level. To ensure the amount of OA
>>going into a space doesn’t go below the ASHRAE 62.1 minimum, I always input
>>the OA Flow per Person and/or Flow per Area at the zone level as well. DCV
>>has always been something I’ve been a little dicey about so any additional
>>suggestions/comments would be great.
>>
>>Thanks,
>>
>>Matthew Larson, LEED AP BD+C
>>Project Engineer
>>Energy Solutions Group
>>E M C Engineers, Inc.
>>Eaton’s Electrical Services & Systems
>>143 Union Blvd, Suite 350
>>Lakewood, CO 80228
>>tel: +1 303 328-3419
>>mobile: +1 303 668-2511
>>fax: +1 303 974-1239
>>MatthewRLarson at Eaton.com
>>www.eaton.com/energysolutions
>>
>>From:equest-users-bounces at lists.onebuilding.org
>>[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg
>>Collins
>>Sent: Tuesday, March 08, 2011 5:53 PM
>>To: Charles Welch; equest-users at lists.onebuilding.org
>>Subject: Re: [Equest-users] EMS Control System Modeling
>>
>>Charles - A quick suggestion for the setback is to try setting your system
>>fans to "cycle on any." Otherwise, your system might not kick on to
>>maintain setback temperatures.
>>
>>
>>Greg Collins
>>GLUMAC | (949) 833-8190
>>
>>From:Charles Welch [mailto:cwelch at capitalreviewgroup.com]
>>Sent: Tuesday, March 08, 2011 4:24 PM
>>To: equest-users at lists.onebuilding.org
>>Subject: [Equest-users] EMS Control System Modeling
>>
>>I am doing an quick estimate for adding EMS control to an existing HVAC
>>system (schools) which incorporate the following measures
>>
>>1) Automatic thermostat setbacks for building occupation
>>2) Demand controlled ventilation
>>3) Economizers
>>
>>Here are my "challenges"
>>1) Simulation with setback temperatures shows no reduction in energy
>>2) I am unsure how to handle DCV
>>3) Simulation with economizers show very little reduction
>>
>>I would appreciate any pointers, suggestions, etc. on what to do here.
>>I would especially appreciate any example files to see how you input the
>>data to get proper results.
>>
>>
>>Thanks in advance for any help.
>>
>>
>>_______________________________________________
>>Equest-users mailing list
>>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>To unsubscribe from this mailing list send a blank message to
>>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/df4ef597/attachment-0002.htm>
More information about the Equest-users
mailing list