[Equest-users] additions in detailed mode for ease of simulation(kirti pabrekar)
Nick Caton
ncaton at smithboucher.com
Mon Mar 14 07:59:49 PDT 2011
Hi Kirti,
See my responses below in red - referenced discussions are attached for
convenience, but note these are 2 among thousands of handy discussions
that can be searched for in the archives ;).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of kirti
pabrekar
Sent: Monday, March 14, 2011 12:14 AM
To: equest-users at lists.onebuilding.org
Cc: equest-users-request at lists.onebuilding.org
Subject: [Equest-users] additions in detailed mode for ease of
simulation(kirti pabrekar)
---------- Forwarded message ----------
From: kirti pabrekar <arkirtipabrekar at gmail.com>
Date: Mon, Mar 14, 2011 at 10:38 AM
Subject: additions in detailed mode for ease of simulation (kirti
pabrekar)
To: equest-users-request at lists.onebuilding.org
hi equesters,
we have a project, that is a 38 storey tower. the tower has 4 podiums
for parking above grade. A gymnasium and health club are placed over the
fourth podium i have attached a rough sketch for better understanding.
the typical residential floor starts above the gym level, all the way
upto 37th floor. please see the sketch attached.
I have simulated a single residential floor plate with systems,
construction, loads etc. Now I need to simulate the entire building ie
all the 37th residential floors and the gym level. We are considering
not to simulate the podium parking levels since no mechanical systems
will be provided. the only loads will be the electrical lighting loads.
could this be counted as the EPD? I'm used to defining unconditioned
parking garage lighting loads without an additional shell - just
schedule those as direct loads to the meter. I can't speak to EPD...
Questions for further model development
1. how do i simulate the entire building with gym level without
going into the wizard mode as we shall lose all input data. Save a copy
of original (A), open copy (B), go back to the wizards and define any
new shells/HVAC systems per usual with unique prefixes and at
appropriate heights (z-coordinates), save, close, open the original (A)
and import the copy (B) in detailed mode [attached discussion walks you
through the importing process], review the added shells/systems and
delete/reassign systems and schedules as appropriate. we have used
floor multipliers in the parametrics and performed simulation. would
this be correct result for the residential component. Floor
multipliers are the way to go conceptually, you should be able to define
this without parametric runs however - double click the shell in the
component tree to edit that figure:
2. how do i add the gymnasium floor level to this model in the detailed
mode. can i use the INP file or should i go on to create the floor by
create child component way. this is a bit difficult method. was
wondering if there is any easier method. i have tried to read the INP
file..to check were the iterations can be made with regards to
this....but it looks too complicated and i cannot understand where to
pitch in my changes....any guidance on this front... Import it - see
above and attached.
3. Does the solar radiation considered by eQUEST at 35th floor is
different that the solar radiation considered at 10 th floor. I'm not
sure of this - I do know eQuest can consider elevation for wind
speed/infiltration calculations, but I haven't read anything that would
make me assume solar radiation is handled differently than at the first
floor... hopefully others may comment to this?
4. the roof of the 4th parking podium is a large landscape for the
tower. where in the model do we input the exterior lighting loads and
podium lighting loads. i understand that the consumption by these loads
is shown as the exterior usage. See attached recent discussion - direct
exterior loads on the meter.
5. how to create the energy meters in the model..and how / where to
assign them...i have never tried them before, but need to get to use
them now...please elaborate at extent. Please elaborate on what you're
trying to accomplish - there are different sorts of meters... I always
define utility meters rates through the wizards and wouldn't recommend
any other way. Sub-meters are sometimes made for various purposes...
again see attached discussion...
6. what are global parameters? Re: "Modeling Procedures Quick
Reference.pdf" under "Help."
7. i have realised that once the model is simulated, a half dozen more
interlinked files are generated, please throw light on the significance
of these....how to derive out of these files? What are you trying to
derive? Here's a recap of the critical ones:
- PD2 - user inputs for use in wizards
- INP - building inputs post-wizards (generated by wizards)
- PRD - parametric run definitions
- SIM - Simulation results
- BDL - Building Description Language - this is a file created on doing
a simulation - it processes the .inp line by line. If an error stops a
simulation you can usually figure out what the problem is by checking
this file out.
--
Regards,
Ar. Kirti Pramod Pabrekar.
IGBC AP, LEED India,
M. Arch,
Environmental Planning and Design.
+91 9821 68 2280
...Green is a commitment...not a competition...
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/63516134/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/63516134/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 12694 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/63516134/attachment-0002.png>
-------------- next part --------------
An embedded message was scrubbed...
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Inputting Elevator and Cooking Loads onSub-Meters
Date: Mon, 7 Mar 2011 10:19:46 -0500
Size: 163081
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/63516134/attachment-0004.eml>
-------------- next part --------------
An embedded message was scrubbed...
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: [Equest-users] eQuest importing mini-gude
Date: Tue, 12 Oct 2010 15:32:17 -0500
Size: 224435
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/63516134/attachment-0005.eml>
More information about the Equest-users
mailing list