[Equest-users] Turn Cooling Off
MatthewRLarson at Eaton.com
MatthewRLarson at Eaton.com
Wed Mar 16 13:43:53 PDT 2011
Josh,
Have you tried changing the Loop Operation in the circulation loop
properties under the Operation tab to "Scheduled" and then specifying a
Cooling Schedule (ON/OFF/TEMP) that disables the loop during the summer
months (with a 0)? For the Fan Coil, make sure your fan schedule uses a
(-1) during the times you want the fan off or if you have the Night
Cycle Control not set to Stay Off, they will cycle on to meet setpoint.
You could also try to make the cooling setpoint ridiculously high during
the summer so there is no need for heat. Is the whole building shut
down during the summer so there is no conditioning going on at all in
the building? Hope one of these comments help or if I'm missing the
boat on your intention, feel free to elaborate.
Thanks,
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com
www.eaton.com/energysolutions
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Talbert, Joshua
Sent: Wednesday, March 16, 2011 1:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Turn Cooling Off
Hello eQuesters,
I am struggling to correctly control my chiller in a chilled water loop
fan coil system. When I look at my SS-E report they are always
indicating cooling (and fans) available all year long. I have created
Fan and Cooling Schedules of very type (ON/OFF, ON/OFF FLAG, ON/OFF
TEMP) to specify that my facility is NOT operating (off) for June, July,
and August, yet no matter what I've done I am still getting energy
consumption to cool during these times!
I've applied my Cooling Availability schedule to the Fan Coils, the
Chiller, the loop Pump and it still seems like something is overriding
the control.
Any insight would be very appreciated.
Thank you and be well.
Josh
Joshua W. Talbert P.E., LEED-AP
Mechanical Engineer
Hallam///ICS
38 Eastwood Dr. Suite 200
S. Burlington, VT 05403
P: (802) 658-4891
F: (802) 658-1457
________________________________
CONFIDENTIALITY NOTICE:
The information contained in this transmission, as well as any
accompanying documents, constitutes confidential and/or legally
privileged information which is the property of Hallam-ICS. The
information is intended solely for the individual entity named on this
transmittal sheet. If you are not the designated recipient, you are
hereby notified that any disclosure, copying, distribution or taking any
action in reliance on this information is strictly prohibited. If you
received this in error, please contact the sender and delete the
material from any computer. Opinions, conclusions and the information in
this message that do not relate to the official business of my firm
shall be understood as neither given nor endorsed by it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/d85f9816/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110316/d85f9816/attachment-0002.jpeg>
More information about the Equest-users
mailing list