Use the formula below to convert Glazing U-value to Conductance.
Conductance = 1/((1/Glazing U)-0.2)
This formula is from the DOE-2 Reference manual.
Best regards,
Gaurav
Gaurav Mehta, LEED® AP BD+C
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Riley Beise
Sent: Thursday, March 24, 2011 2:12 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Simplified Method Glass Conductance Entry
Hi all,
I'd like to be able to enter my total glazing U values in one place for simplicity. I set my frame widths to zero and defined my window glass type in "simplified" where I entered my total window U value in the "Glass Conductance" field. When I check my LV-D report it shows my windows having a lower U value than what I entered. I understand there are some variables at play here that are likely the cause (air film resistance and windspeed of rating (summer vs winter as shown in the topic help). I don't understand what is going on here.
So,
Can someone shed some light on why my LV-D window U values don't match my "Glass Conductance" value in these circumstances?
And, how would you recommend I enter my windows if I have the overall U value already from product data?
Thanks
Riley
___________________________________
Riley Beise, EIT, LEED GA
Green Building Specialist
Enermodal Engineering Ltd.
602-2303 4th St. SW, Calgary AB T2S 2S7
p. 403-244-0474 ext. 435
f. 403-244-0475
e. rbeise at enermodal.com<mailto:bpapau at enermodal.com>
www.enermodal.com<blocked::http://www.enermodal.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110324/fc9a3b6a/attachment-0002.htm>
More information about the Equest-users
mailing list