[Equest-users] question about inefficiency of duct

Andy Phelps aphelps at barnesanddodge.com
Wed Mar 30 06:11:41 PDT 2011


If you’re looking to see what change in temp you have based on a length of duct, insulation, etc, check out:

 

http://www.mcgillairflow.com/textDocs/techTools/converted/thermalData1.php

 

This calculator is really meant for exterior applications as well as determining if condensation will occur (and you have to use their preset products for insulation thickness & k values), but it can be a quick reference for us looking to see what an avg heat loss might be in a duct system.  (I’m sure there’s a reference to the ASHRAE handbooks, but I’m drawing a blank right now…)

 

What I am unsure of in eQuest is how it uses Supply Duct UA and Duct Delta T.  If heat is lost in the duct, is it gained in the ceiling space or plenum??  If that is the case, then the arguments below that the overall net effect is negligible is a good one.  However, fan energy will increase since the delta T of the supply air to room air decreases.

 

 

Andy Phelps, PE, LEED AP | BARNES & DODGE, INC. | aphelps at barnesanddodge.com | (o) 913-321-6444 | (c) 913-710-7915 | 

The information contained in this electronic message is confidential and is or may be protected by trade secret protections, and/or other applicable protections from disclosure.  If the reader of this message is not the intended recipient, you are hereby notified that any use, dissemination, distribution or reproduction of this communication is strictly prohibited.  If you have received this communication in error, please immediately notify us by calling 913-321-6444, or by e-mail to front at barnesanddodge.com <mailto:front at barnesanddodge.com> , and immediately delete this e-mail message and any attachments thereto. Although this e-mail message and any attachments are believed to be free of any virus or other defect that might negatively affect any computer system into which it is received and opened, it is the responsibility of the recipient to ensure that it is virus free and no responsibility is accepted by Barnes & Dodge, Inc. for any loss or damage arising in any way in the event that such a virus or defect exists. Thank you.

 

 

 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Tuesday, March 29, 2011 7:32 PM
To: Nick Caton; McArdle, Mike; xiaoyang shi; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] question about inefficiency of duct

 

Nick:

For a supply duct passing through a plenum return ceiling during the cooling season, the temperature difference between the supply air and return air can be as much as 25 degrees.

During the heating season, this difference could be as much as 30 degrees during morning warm up.

Paul Diglio

 

________________________________

From: Nick Caton <ncaton at smithboucher.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; "McArdle, Mike" <Mike.McAardle at state.vt.us>; xiaoyang shi <xs2144 at gmail.com>; equest-users at lists.onebuilding.org
Sent: Tue, March 29, 2011 8:03:32 PM
Subject: RE: [Equest-users] question about inefficiency of duct

I think Mike’s general point is fair and isn’t to be taken in absolutes.  

 

When a ducted return air stream is passing through a conditioned space or plenums/chases in between other conditioned spaces, it’s probably a safe bet to claim any duct gains/losses are *negligible* (not nonexistent), particularly if said return ducts are insulated, due to the relatively small delta-T.

 

On the other hand, winter losses and summertime gains at extreme temperatures may be considerable if any ductwork is routed exterior to the building, even if insulated.  

 

Xiaoyang, if you wish to calculate it as a percentage at design conditions:   ( U x A x deltaT )DUCT / (total building heating or cooling load) x 100

 

If you wanted to model such exterior duct heat losses/gains in eQuest… I haven’t considered that before – but depending on your system setup, it might be as simple as  a small exterior wall surface with appropriate U-value and area equal to the duct surface area… in the event the solar loads incident on the duct might be significant, make a point to correctly locate the surface in 3D (over the roof, along a wall, etc.) to avoid any incorrect self-shading from other surfaces.

 

If anyone has delved into this and knows a better/simpler way please do share =).

 

~Nick

 

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Tuesday, March 29, 2011 4:59 PM
To: McArdle, Mike; xiaoyang shi; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] question about inefficiency of duct

 

Michael:

"if the air in duct is the same air as the air being supplied to the space, there is no net effect"?  What do you mean by net effect?

The duct heat loss/gain depends on the difference of the temperature of the air in the duct and the temperature of the air surrounding the outside of the duct.  It is highly unlikely that these temperature will be the same.

Paul Diglio

 

________________________________

From: "McArdle, Mike" <Mike.McAardle at state.vt.us>
To: xiaoyang shi <xs2144 at gmail.com>; "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Tue, March 29, 2011 5:39:40 PM
Subject: Re: [Equest-users] question about inefficiency of duct

Dear xiaoyang shi 

 

It Depends on the temperature differentials between air in duct and space and insulation thickness 

 

But more importantly , if the air  in duct is the same air as the air being supplied to the space there is no net effect 

 

 

Thank you,  Sincerely,

 

Michael J. McArdle , P.E.

Buildings Engineer II, Project Manager 

State of Vermont, 

Buildings and General Services (BGS)

2 Governor Aiken Avenue

Montpelier, Vt. 05633

 

Office: 802-828-5650;  cell: 802-272-4828

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of xiaoyang shi
Sent: Tuesday, March 29, 2011 5:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] question about inefficiency of duct

 

Hi folks,

In the winter time, some heat loss in HVAC is from duct.

What is the percentage of heat loss through the duct to the total building heat load, due to the inefficiencies of duct delivery system?

Thank you guys.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110330/6f977feb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110330/6f977feb/attachment-0002.jpeg>


More information about the Equest-users mailing list