[Equest-users] Odd peak cooling day
Charles Land
cland at geo-marine.com
Mon May 2 11:55:23 PDT 2011
I see that this is the peak load for a single space which is a core space. Does this space have any exterior walls, and is there a 2nd floor above this space. If its an interior area the outside weather conditions shouldn't have any effect on the cooling load for this space.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Travis Rhodes
Sent: Monday, May 02, 2011 2:40 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Odd peak cooling day
I don't know where I've gone wrong, but my peak cooling day is happening in December. The output is saying that there is a huge internal heat load from occupants on that day. As far as I can tell the occupant schedule is correct. Any insight into this is appreciated.
[cid:image001.jpg at 01CC08D8.9B766ED0]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110502/3f7f8437/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 10697 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110502/3f7f8437/attachment-0002.jpg>
More information about the Equest-users
mailing list