[Equest-users] Modeling regular curtain wall systems
Arpan Bakshi
arpanbakshi at gmail.com
Fri May 6 06:03:14 PDT 2011
Sounds like a good compromise. I'm concerned the corner zones would
take on the brunt of the frame/glass disparity, creating a large
contrast of skin loads on the perimeter.
Arpan Bakshi, LEED AP BD+C
YRG sustainability
On May 6, 2011, at 8:35 AM, "Bishop, Bill" <wbishop at pathfinder-ea.com>
wrote:
> I typically model curtain walls as a single window per exterior wall
> surface, and increase the frame width to make the frame area equal
> to the total non-glazed area of the window opening.
>
> I select a glass type from the DOE-2 window library based on the
> closest match of U-value and SHGC to the actual glazing selection.
>
>
>
> Bill
>
>
>
> <image003.jpg>
>
>
>
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-
> users-bounces at lists.onebuilding.org] On Behalf Of Arpan Bakshi
> Sent: Thursday, May 05, 2011 8:29 PM
> To: Mark Darrall
> Cc: equest-users
> Subject: Re: [Equest-users] Modeling regular curtain wall systems
>
>
>
> Mark, in the interest of time, you can accomplish what you would
> like to through the Building Shell Wizard --
>
>
>
> 1. If you already have a Window 4/5 file from the manufacturer,
> attach it in Wizard Screen 6 under Glass Category.
>
>
>
> 2. If you do not have this, right-click Glass Category and under
> Tutorials and Reference, and navigate to DOE 2 Glass Library (xls).
> You will be able to find something comparable to your glass type
> here. Select a Frame Type and Frame Wd (in) which matches your
> curtain wall assembly.
>
>
>
> 3. Under Window Dimensions, Positions and Quantities, you can
> specify a Typ Window Width (ft). Now comes the shortcut to avoid
> Custom Window/Door Placement. If your fenestration design consists
> of an irregular, custom pattern, count the number of vertical
> mullions you have, and divide the full width of the curtain wall by
> that number. Enter that number into Typ Window Width (ft). Though
> your curtain wall will not have the same appearance in the 3D View,
> you are provided the same length of lineal feet of window frame,
> which will result in the same overall assembly U factor.
>
>
>
>
>
> On Thu, May 5, 2011 at 7:55 PM, Mark Darrall <MDarrall at a2so4.com>
> wrote:
>
> Thank you! I’m working against a pretty hard deadline and don’t
> really have time to learn two more software packages. I found some b
> asis of design information for both the curtain wall and glazing – c
> an I use manufacturer’s design guide graphs and calculations? The gr
> aphs are “per AAMA 507.” They also have charts for NFRC 100
> overall U factors and NFRC 200 SHGC and VT.
>
>
>
> I think the LEED reviewers just want to make sure we’re accounting f
> or the frames and not just getting COG.
>
>
>
> Take care!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> <image004.jpg>
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> Please consider the environment before printing this e-mail.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it
> are confidential and intended solely for the use of the individual
> or entity to which they are addressed. If you are not the intended
> recipient, you may not review, copy or distribute this message. If
> you have received this email in error, please notify the sender
> immediately and delete the original message. Neither the sender nor
> the company for which he or she works accepts any liability for any
> damage caused by any virus transmitted by this email.
>
>
>
> From: Alex Krickx [mailto:akrickx at seriousmaterials.com]
> Sent: Thursday, May 05, 2011 7:47 PM
> To: Carol Gardner; Mark Darrall
> Cc: equest-users
> Subject: RE: [Equest-users] Modeling regular curtain wall systems
>
>
>
> You can create curtainwall systems in Window and Therm – but I
> don’t believe that eQUEST will import any of the frame conductance d
> ata. I think the best way to model curtainwall systems is to model t
> he frame in THERM and WINDOW5, create a DOE2 report file – then impo
> rt that file into eQUEST and manually edit the frame width and condu
> ctance to match what you calculated in WINDOW5/THERM.
>
> Alex
>
>
>
> Alex Krickx, LEED AP
>
> Building Energy Specialist
>
> <image005.jpg>
>
> 1250 Elko Dr, Sunnyvale, CA 94089
>
> (t) 408.541.8124
>
>
>
> Warning: The information contained in this e-mail may be privileged
> attorney-client communications or attorney work product and/or
> proprietary and confidential. If the reader of this message is not
> the intended recipient then you have received it in error and any
> review, distribution or copying of this message is prohibited and
> you are to notify us immediately by reply e-mail and delete the
> original message immediately.
>
>
>
>
>
>
>
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-
> users-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
> Sent: Thursday, May 05, 2011 4:43 PM
> To: Mark Darrall
> Cc: equest-users
> Subject: Re: [Equest-users] Modeling regular curtain wall systems
>
>
>
> Intriguing question. I did just a little looking around and found: windows.lbl.gov/software/NFRC/NFRCSim6.3-2010-Manual.pdf
> .
> which is a link to the user manual for Window and Therm. Check it
> out. You can create things, windows,etc., maybe even curtainwalls,
> using Window and import them into eQUEST
>
> Carol
>
> On Thu, May 5, 2011 at 4:19 PM, Mark Darrall <MDarrall at a2so4.com>
> wrote:
>
> Hi!
>
>
>
> What’s the best way to input a curtain wall system to allow for the
> repetitive vertical mullions? I can calculate system U factor based
> on the area of vision glass : overall area, but I don’t see a way to
> input that directly…unless:
>
>
>
> If the vertical mullions are already captured in the system U factor
> can I just ignore it and treat it like one huge picture window? So
> at FRAME-WIDTH I would just enter the width and properties of the
> perimeter frame and then at GLASS-CONDUCTANCE enter the corrected U-
> factor for the system?
>
>
>
> I did search this in onebuilding.org, but didn’t see it addressed.
>
>
>
> Thanks!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> <image004.jpg>
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> Please consider the environment before printing this e-mail.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it
> are confidential and intended solely for the use of the individual
> or entity to which they are addressed. If you are not the intended
> recipient, you may not review, copy or distribute this message. If
> you have received this email in error, please notify the sender
> immediately and delete the original message. Neither the sender nor
> the company for which he or she works accepts any liability for any
> damage caused by any virus transmitted by this email.
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
>
>
>
>
>
> Arpan Bakshi LEED AP BD+C
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110506/9350047c/attachment-0002.htm>
More information about the Equest-users
mailing list