[Equest-users] Creation of Scroll Air Cooled Chiller PerformanceCurve
MatthewRLarson at Eaton.com
MatthewRLarson at Eaton.com
Mon May 9 08:13:22 PDT 2011
Enrique,
The EIR-FPLR performance curve you have defined appears to be the wrong
Curve Type. The default curve type for the type of chiller you defined
is a "Bi-Quadratic in Ratio & DT" Curve Type. This curve has 6
coefficients and two variables. I'm thinking you can use the a, b, and
c coefficients you have and then put zeros for the d, e, and f
coefficients. The equipment in eQuest seems to be rather picky about
the Curve Types so you have to make sure you select the correct one.
Hope this works.
Thanks,
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com
www.eaton.com/energysolutions
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Enrique
Chavez-Castro
Sent: Saturday, May 07, 2011 5:50 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Creation of Scroll Air Cooled Chiller
PerformanceCurve
Dear E-Quest Team Members,
Could anyone please tell me the steps how to create the above?
I have inputted the coefficients per attached file but it does not seem
to t work.
Please see error in slide 6.
Sincerely,
Enrique
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110509/243be71b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110509/243be71b/attachment-0002.jpeg>
More information about the Equest-users
mailing list