[Equest-users] Exterior Shades
Greg Collins
GCollins at glumac.com
Tue May 10 12:20:52 PDT 2011
There is no standard formula for doing this. A correction factor for the SHGC could be calculated, but this factor would change significantly depending on geographic location (sun angles), and would not give you accurate results at an hourly level (accurate for annual only). If you're trying to avoid modeling all of the shades, you could pick one typical window for each exposure to model, and apply those results to all of them, but I'd recommend against that.
This is when modeling geometries in Revit comes in handy ;)
Greg Collins
GLUMAC | (949) 833-8190
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sambhav tiwari
Sent: Tuesday, May 10, 2011 4:38 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Exterior Shades
Hi All,
My Glazing is having exterior shade from all four side it
is like 2 overhangs one at top and other at bottom of glazing and two
side fins. is this any formula to calculate reduction in shgc value
by all four shades as it is just by one overhang.
Thanks
Sambhav