[Equest-users] question about water "Design Flow"
Grammy Jiang
grammy.jiang at gmail.com
Wed May 11 18:27:21 PDT 2011
Hey, Xiaoyang,
View the report *PV-A: Plant Design Parameters*. If there is water loop in
the model, there will be a "circulation loops" section which contain a
keyword "Loop Flow (Gal/Min)".
*Loop Flow (Gal/Min)*:is the flow at the larger of the HEATING-CAPACITY or
COOLING-CAPACITY, at the design loop temperature change. (Page 167, DOE2.2
Volume4: Libraries & Reports)
Best Regards,
Grammy, Jiang
On Thu, May 12, 2011 at 03:45, xiaoyang shi <xs2144 at gmail.com> wrote:
> Hi folks,
>
> From equest output Air-side HVAC summary, we can get the design air flow
> rate "cfm".
>
> However, in the Water-side HVAC summary, there is nothing. Where could we
> get the water design flow rate?
>
> Thank you very much.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110512/677d295e/attachment-0002.htm>
More information about the Equest-users
mailing list