[Equest-users] [GUIDE] Add a zone in detailed mode
Nick Caton
ncaton at smithboucher.com
Mon May 16 09:22:26 PDT 2011
Hey Brad,
Sounds like you've tread a number of paths already!
There are many ways to skin this cat. Following is one procedure that is pretty comprehensive (doesn't cut corners), and is relatively quick/easy for rectilinear spaces. There are simpler/faster approaches out there appropriate for different situations, but this covers most cases.
For review before starting: Any new zone needs a space to be associated with, so to 'split' an existing zone, you first need to 'split' its referenced space... that's the biggest part of the job.
Highlight the target space in the component tree under the 'building shell' tab. You can easily find it by selecting the space or one of its surfaces in the 2D or 3D views. If possible, switch to 3D view and orient so that you can observe your target space during the following procedure.
1. Double-click the space in the tree. If you built this from the wizards, you'll see a referenced space polygon "i.e. EL1 Space Polygon ##." Make a mental note.
2. Close the dialog, and double click on that space polygon in the component tree.
3. Here you'll see that polygon's vertices one after the other. Our goal is to split the space down the middle, so all you need to do is modify a couple vertices. Sketch it out the vertices if you need to, on a scratch pad. As you mess with the polygon vertices, you will see the results of your handiwork on closing the dialog in the 3D view. Following illustrates turning a 40ft long space into a 20ft long space:
[Notice!] Not only did the space (which we can't see in this view) change geometries, but so did the associated plenum space and all associated surfaces. That's because they all reference this same polygon.
4. Right-click the modified space à "Create another space..." à in the dialog, select 'copy existing component' à check that the referenced space is selected à tick the box for create/copy all child components à click the 'OK' button. For this exercise, give your space a name you'll remember/recognize so you can find it easily in the lists. Repeat for the associated plenum space.
5. What you have right now is a set of spaces, identical in every regard, that are right on top of each other geometrically. If you wish, you can move your newly created space about by modifying its x/y/z coordinates (double click the new space in the tree). Again, the 3D view will illustrate what's going on, if desired. Note: the space polygon vertices you just modified may be helpful in determining how much to adjust x/y to make everything sync up perfectly... in this case, I simply adjusted the plenum and ground-level space y-coordinate by 20ft.
6. Jump to the 'air-side HVAC' tab, right click the original zone à create another thermal zone à copy existing component. A dialog will prompt you for a space to assign, and you'll have a list of all unassigned spaces to choose from. Select the new space, repeat for the plenum zone.
Now all spaces/zones are created and located! Review both and tweak as desired to correct internal loads, assign schedules, or whatever else should differentiate them. Consider and judge whether it's necessary to redefine/reassign any surfaces for adjacent zones. Reassign the new zones' parent system, or create a new one if necessary.
...And there you have it! Note there are potentially faster methods of "winging it" where you can just modify the defaulted area/volume and the "pertinent" variables of a space/zone before copying (i.e. occupancy/loads/surface areas), but be cautioned that such approaches can easily end up being more work in the long run should you need to modify everything in the end.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brad Robinson
Sent: Sunday, May 15, 2011 3:18 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Add a zone in detailed mode
Due to some changes in the floor plan, I need to add another zone by splitting one zone into 2. Currently I am in detailed mode and prefer to not switch back. I can change the shape of the existing zone to a smaller one no problem. The issue comes when trying to create a new zone. I have tried several methods but end up with either:
a) I tried copying an existing space polygon, but it does not actually seem to be a copy, as when I move points, it changes the shape of the original space as well
b) Tried to create a zone from scratch using a BOX shape, but whenever I finish editing the vertices, I gives me the error "Unable to post date to the BDL"
c) One time I successfully created a shape, but it seems to move depending on what view I am in. For instance, in polygon view, it is in the correct spot, but when I go to 2D mode, it is located completely outside of the building.
I'm not sure what the approach is to do this. Any advice would be greatly appreciated. Thanks.
Brad Robinson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 77136 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 28912 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 40463 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0020.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 100506 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0021.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8615 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0022.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8507 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0023.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 81324 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0024.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4369 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0025.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4420 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110516/1065940f/attachment-0026.png>
More information about the Equest-users
mailing list