[Equest-users] Appendix G. supply fan power and altitude adjustment
Bishop, Bill
wbishop at pathfinder-ea.com
Wed May 18 06:22:30 PDT 2011
Nick,
Thanks for forwarding the previous post - I should've searched the
archives first.
I see merits to both schools of thought. My preference for now will be
to set project altitude to zero. The air flow and fan power reported in
SV-A will be consistent with the calculated/entered value for baseline
fan power (in kW/cfm).
Bill
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Tuesday, May 17, 2011 6:13 PM
To: Bishop, Bill; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Appendix G. supply fan power and altitude
adjustment
Hey Bill,
These altitude shenanigans eQuest likes to play in the airflow/coil
calculations are a potentially messy issue when it comes to baseline
calcs and LEED reviewers.
Attached thread pretty much covers the issue inside and out from
multiple perspectives.
There are a 2 schools of thought:
1. Set project altitude to '0' - this corrects all airflows, but
you'll find coil capacities are sized slightly differently (this has
been a working approach for LEED reviewers in my experience)...
2. Divide all entered airflows by the altitude factor for the
project (listed on those system reports). A more cumbersome solution,
but I gather this will correctly trick eQuest into doing the intuitive
thing with regard to airflow/coil sizing.
My sense is this is one of those things fundamental to DOE-2 that won't
easily change, but I've said before - it would be a great 'feature' to
add in future releases to have an option to treat all entered capacities
are relative to the site elevation, instead of sea level.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Tuesday, May 17, 2011 2:49 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G. supply fan power and altitude
adjustment
The supply cfm reported in SV-A is corrected for altitude, but the fan
power on the same report is for sea level. So if, for example, you enter
0.0003 kW/cfm for Appendix G Baseline System 1 and 2 fan power, the SV-A
reported fan power is low relative to the SV-A flow rate. (This was
noticed in a LEED review and I was asked to verify the fan power
calculations.)
Can/should I be multiplying the baseline fan power allowance by the
altitude factor (also reported on SV-A)?
Thanks,
Bill
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/0ac76fb4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/0ac76fb4/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/0ac76fb4/attachment-0005.jpeg>
More information about the Equest-users
mailing list