[Equest-users] LEED and outdoor air rates
Bishop, Bill
wbishop at pathfinder-ea.com
Wed May 18 07:11:14 PDT 2011
Brad,
Does LEED Canada require ASHRAE 90.1, Appendix G for modeling? Appendix
G requires that, "Mininum outdoor air ventilation rates shall be the
same for the proposed and baseline building designs." I manually enter
the OA flow rates in all zones, keeping them identical between the
proposed and baseline cases, to meet this requirement.
Regards,
Bill
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brad
Robinson
Sent: Tuesday, May 17, 2011 5:53 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED and outdoor air rates
My proposed building is a long term care facility with a 100% OA unit
serving the patient rooms. The generated baseline LEED model does not
reflect this above average OA requirement. For the purposes of LEED
Canada, would the approach be to increase the OA flow rates for each
space equal to the proposed design? It would seem to me both cases
should be modelled the same in this respect. Thanks.
Brad Robinson.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/fe0d84c3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/fe0d84c3/attachment-0002.jpeg>
More information about the Equest-users
mailing list