[Equest-users] peak heating demand
deepika khowal
deepika.khowal at gmail.com
Wed May 18 14:44:23 PDT 2011
Thanks Alex
I think the explanation you gave was very clear.
so when we design HVAC system, which loads we should consider?
for windows with better R-values, the peak load may b lesser but its overall
annual demand will be higher.
how to account for this in HVAC sizing?
On Wed, May 18, 2011 at 12:02 PM, Alex Krickx
<akrickx at seriousmaterials.com>wrote:
> Hi Deepika,
>
>
>
> I’m not sure how eQUEST calculates loads, but I can imagine a scenario
> where your results make sense:
>
>
>
> Peak heating load probably happens at night/early in the morning, right? So
> it probably depends on insulation (R-value) and not solar gains (SHGC). My
> guess is the window with the higher peak demand has low R-value (since you
> need lots of heat to make up for losses). But this window could have a high
> SHGC, so when the sun is out you benefit from passive heating (and have
> lower annual heating demands).
>
>
>
> I’m guessing your other window (with lower peak heating) has a better
> R-value - it retained heat better. This window may have a lower SHGC
> (possibly due to additional low-e coatings) and so it get less passive
> heating throughout the year and needs more heat to be added to the building
> during daytime hours.
>
>
>
> This will depend on the windows you’ve modeled, building type and climate.
> Perhaps if you share some more info on the project the answer will present
> itself.
>
>
>
> Regards,
>
> Alex Krickx
>
>
>
> Alex Krickx, LEED AP
>
> Building Energy Specialist
>
> [image: email_sig]
>
> 1250 Elko Dr, Sunnyvale, CA 94089
>
> (t) 408.541.8124
>
>
>
> *Warning:** The information contained in this e-mail may be privileged
> attorney-client communications or attorney work product and/or proprietary
> and confidential. If the reader of this message is not the intended
> recipient then you have received it in error and any review, distribution or
> copying of this message is prohibited and you are to notify us immediately
> by reply e-mail and delete the original message immediately.*
>
>
>
>
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *deepika khowal
> *Sent:* Wednesday, May 18, 2011 11:19 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] peak heating demand
>
>
>
> Hi all
>
> I am modeling the performance of different glazing types in a building.
>
> I realized for one glazing, the peak gas demand is lower than other glazing
> but total heating energy is higher?
>
> how does equest calculate these loads and energy?
>
> Thanks
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/f3f41a58/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5602 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/f3f41a58/attachment-0002.jpeg>
More information about the Equest-users
mailing list