[Equest-users] how to serve same zone with two different AHU.
Nick Caton
ncaton at smithboucher.com
Mon May 23 07:37:06 PDT 2011
Hi Ashok!
You're driving against a fundamental limitation of DOE2/eQuest... Your
workaround options depend on what exact situation you're trying to
emulate.
Example: If I am modeling a bedroom which has a window condensing unit
(thermostat in the room), but is also served by a central HVAC
furnace/AC (thermostat elsewhere), I might choose to split the bedroom
into two spaces, separated by an air wall. This approximates the room
as two spaces thermally connected as one, but permits the assignment of
multiple systems onto the room (and correct locations of their
thermostats). I can ensure all the envelope/solar/skin loads are on one
half, to be handled by the window unit, by carefully selecting where to
split the space.
That may be an acceptable approach for your current case, but if not,
you'll need to supply us with more info about what systems are and why
the above won't work.
Best of luck,
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ashok
Singh Tanwar
Sent: Monday, May 23, 2011 5:40 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] how to serve same zone with two different AHU.
Dear all,
i have some different zones, in which some zones are served by two
AHU's. How can i modeling it. i can not make both of them child
component, because they are already a child component of another zone's
AHU.
Plz Guide me.
Regards
Ashok Singh Tanwar
M.Tech. (Energy Engg.)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/76e0f381/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/76e0f381/attachment-0002.jpeg>
More information about the Equest-users
mailing list