[Equest-users] input parameters for area lights and miscellaneous equipments.

Patrick J. O'Leary, Jr. poleary1969 at gmail.com
Mon May 23 12:44:32 PDT 2011


i used to not separate them out either but 2 leed reviews ago i received 
a comment about it.  being active about it i just did my next submittal 
with it broken out & then found out (via a cir from 2007) that the 
reason they're asking is the reviewers want to make sure credit is only 
taken for the tradable exterior lighting power.  exterior non-tradable 
lighting power is energy neutral.  i.e. you can't use the designed, 
lower than leed allowed non-tradable in the proposed model and the 
higher 90.1 allowable in the baseline.  makes no sense to me what so 
ever.  as far as i'm aware non-tradable means just that - you can't 
trade it for higher lighting power elsewhere, not that when simulated 
you can't claim credit for using less than what is allowable.

but the cir says otherwise, along with 10 or so other things.  april 25, 
2007.  also noted in the advanced energy modeling guide for leed common 
errors section on page 27, last row, last bullet item, "Nontradable 
surfaces are not modeled with lesser of nontradable surface and 
installed lighting power for each nontradable surface, as required."

without wanting to change the topic to water savings note question 9 
(they put in 11 questions in one cir), if you didn't know you can't 
claim energy savings due to using low flow fixtures.  so if you're using 
less hot water you can't reduce the amount of water circulated to claim 
credit on the electrical (and/or gas) side of things.

cir from april 25, 2007 states 2 important things:
   Inquiry Number:    5261
   MPR/Prerequisite/Credit:     EAc1: Optimize Energy Performance
   Posting date:     4/25/2007

[REVISED 10/30/07 to allow energy savings for exterior lighting.] ...

question:
7. Exterior Lighting Will USGBC for LEED 2.2 allow credit for exterior 
lighting that is more efficient than the new mandatory provision for 
exterior lighting in 90.1-2004 section 9.4. Appendix G does not address 
how exterior lighting should be modeled for the baseline, and therefore 
the default is that it should be modeled the same as the design and no 
credit for savings could be taken

answer:
7. Yes, project teams can take credit for efficient exterior lighting 
within ASHRAE 90.1 Appendix G. Credit may only be taken for the tradable 
surfaces listed in ASHRAE 90.1-2004 Table 9.4.5. All other exterior 
lighting must be modeled identically in the Baseline and Proposed case. 
The Baseline case exterior lighting power allowance should be calculated 
using the methodology outline in Section 9.4.5.

question:
9. DHW Usage Reduction Will USGBC for LEED 2.2. allow the approach to 
claim domestic hot water energy cost reduction based on low flow 
fixtures, relative to EPACT standard allowed fixture flows from earlier 
LEED 2.1 rulings. Another approach would be to adopt 90.1-2004 addendum 
a) revision to Table 3.1 Baseline 11. labeled as a revision to G4.3 
under the older numbering convention.

answer:
9. No. Credit for saving water is already granted in the Water 
Efficiency section of the LEED Rating System. The Domestic Hot Water 
(DHW) loop will be sized for design flows and the PRM does not allow 
credit for changing loop flows for DHW.


On 5/23/11 11:12 AM, Nick Caton wrote:
>
> Interesting!  I feel I should share some contrary experience, since it 
> may save you guys some time in the future =):
>
> I've never separately metered tradable vs. non-tradable exterior 
> lighting within the model itself, nor been asked to.
>
> I am however used to submitting my interior/exterior LPD calculations 
> (via COMcheck or excel spreadsheet) alongside the other documentation, 
> and entering those tallies into the model.  These separate 
> calculations do distinguish tradable vs. non-tradable, as well as any 
> exemptions/allowances used, so perhaps that's why I've never been 
> asked to separately meter/report within the model.
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com_ _
>
> *From:* Patrick J. O'Leary, Jr. [mailto:poleary1969 at gmail.com]
> *Sent:* Monday, May 23, 2011 10:36 AM
> *To:* Nick Caton
> *Subject:* Re: [Equest-users] input parameters for area lights and 
> miscellaneous equipments.
>
> just don't forget, for leed purposes, to break out the exterior 
> lighting into tradable and non-tradable by putting them on different 
> meters.  you can't do this in wizard mode though, only the detailed mode.
>
> On 5/23/11 7:53 AM, Nick Caton wrote:
>
> Soham and Kirti,
>
> Exterior lighting:  W/SF as entered in the wizards is multiplied by 
> the corresponding shell's area in which you're assigning it.  Quirky, 
> but if you keep that in mind you can avoid the extra step of 
> correcting in detailed.  It's an easy mistake to enter installed Watts 
> or kW in the wizard (that seems intuitive to me also).
>
> Miscellaneous loads and LPD's in the wizards are also handled on a 
> W/SF basis, but for each space.  You can override the defaults if you 
> wish to:
>
> LPD is entered for each occupancy type, and those occupancy types are 
> then assigned to each zone, if you fully utilize the DD wizards.  You 
> may be as detailed (or not) in assigning your occupancy types as you 
> feel comfortable/necessary.
>
> For miscellaneous equipment, I suggest referencing the 90.1 User's 
> manual for plug load W/SF in the context of a LEED/90.1 model.  You 
> can similarly enter a uniform W/SF value for each occupancy type and 
> that will translate straight into detailed.
>
> Miscellaneous loads beyond plug loads (ex: elevators, process 
> equipment...) are something I usually handled in detailed mode, where 
> I can directly edit/create/import the associated scheduling and assign 
> names I can easily track/reference/document.
>
> An extra reminder:  You can streamline the process of defining 
> exterior lighting schedules by saving re-useable ones in an .inp file 
> and importing them from previous projects ;).  More discussion in the 
> archives if you're curious!
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com_ _
>
> *From:* equest-users-bounces at lists.onebuilding.org 
> <mailto:equest-users-bounces at lists.onebuilding.org> 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Soham Babu
> *Sent:* Monday, May 23, 2011 8:14 AM
> *To:* kirti pabrekar; equest-users-request at lists.onebuilding.org 
> <mailto:equest-users-request at lists.onebuilding.org>; 
> equest-users at lists.onebuilding.org 
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] input parameters for area lights and 
> miscellaneous equipments.
>
> Kirti,
>
> We can give actual exterior load by assigning it to the electric meter 
> as screen shot 1, before that you have to create the exterior lighting 
> schedule as shown in screen shot 2 day, week & annul schedule, then 
> you can assign the calculated value in electric meter in detail mode. 
> Regarding the miscellaneous equipment leave eQUEST default as shown in 
> screen shot 3 , otherwise if you enter the value by yourself it should 
> be same in baseline & proposed. Regarding LPD for Baseline ASHRAE 90.1 
> value & for Proposed Actual electrical design. I hope this helps you...
>
> Kind Regards
>
> Soham babu
>
> *From:* equest-users-bounces at lists.onebuilding.org 
> <mailto:equest-users-bounces at lists.onebuilding.org> 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *kirti pabrekar
> *Sent:* Monday, May 23, 2011 10:05 AM
> *To:* equest-users-request at lists.onebuilding.org 
> <mailto:equest-users-request at lists.onebuilding.org>; 
> equest-users at lists.onebuilding.org 
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] input parameters for area lights and 
> miscellaneous equipments.
>
> Dear all,
>
> I have a query about assigning the area light values and miscellaneous 
> equipment values in eQuest.
>
> While assigning the area lights, exterior loads and miscellaneous 
> equipment loads; I input the necessary power densities in the wizard 
> mode. However  I have realized that, the exterior lighting load (w/sf) 
> input in the Wizard mode is multiplied by the building area (all 
> floors) and becomes a direct kW load on the electric meter. This 
> directly resulted in very high numbers for the exterior usage in the 
> simulation results. This is erroneous in my case and I have figured 
> out a way to correct it by calculating the actual exterior load figure 
> and assigning it to the electric meter and updating it with a 
> necessary schedule.
>
> I was wondering if the software considers a similar analogy for 
> calculating the area lights and the miscellaneous equipment figures in 
> the simulation results as it does for the exterior usage. If that is 
> so, i am sure my results are way too wrong or over board. what would 
> be correct way/s to input the area light and miscellaneous equipment 
> figures. Please find attached the .INP file for your reference.
>
> Thanks for your time in anticipation.
>
> -- 
>
> Regards,
> Ar. Kirti Pramod Pabrekar.
>
> IGBC AP, LEED India,
> M. Arch,
> Environmental Planning and Design.
>
> /...Green is a commitment...not a competition.../
>
>   
>   
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG  <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>    
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/b8bf4e8d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/b8bf4e8d/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11702 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/b8bf4e8d/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 12175 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/b8bf4e8d/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 10506 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110523/b8bf4e8d/attachment-0011.jpeg>


More information about the Equest-users mailing list