[Equest-users] MIN AIR SCH
Rob Hudson
rdh4176 at gmail.com
Tue May 24 10:45:07 PDT 2011
When i set the high temperature limit to 65 deg, this caused the economizer
to operate as it is supposed to.
Hope this helps for future economizer issues.
Rob
On Tue, May 24, 2011 at 1:41 PM, Rob Hudson <rdh4176 at gmail.com> wrote:
> I have entered no space inputs for OA, everything has been entered at
> System level. I have a dual temperature economizer set up.
>
> Rob
>
> On Tue, May 24, 2011 at 1:38 PM, Arpan Bakshi <arpanbakshi at gmail.com>wrote:
>
>> Space level inputs will override system level inputs here. May want to
>> check those.
>>
>>
>>
>> On Tue, May 24, 2011 at 12:35 PM, Rob Hudson <rdh4176 at gmail.com> wrote:
>>
>>> When trying to set up a space to have economizer mode using the schedule,
>>> i can't seem to make it work.
>>>
>>> When i enter the value 0.001 as requested by the help files, to enable
>>> economizer mode and let the unit go to 0% during the unoccupied periods, it
>>> doesn't work.
>>>
>>> When i enter -999 as requested by the help files to allow my stated OA
>>> ratio to rule (33% in this case) it doesn't allow it to go to 100% OA and
>>> therefore i get unmet hours.
>>>
>>> If i set the value to 1 at all times, then i get 100% OA during the
>>> summer, which is not advised.
>>>
>>> Any help is appreciated,
>>>
>>> --
>>> Rob Hudson
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>>
>> --
>>
>>
>> Arpan Bakshi,* *LEED AP BD+C
>>
>>
>
>
> --
> Rob Hudson
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110524/041230c3/attachment-0002.htm>
More information about the Equest-users
mailing list