[Equest-users] Sizing runs in baseline model
David Eldridge
dse at grummanbutkus.com
Sat May 28 14:25:00 PDT 2011
How about the SS-H report? That will show the fan energy, as well as DX
cooling and furnace heating for specific AHU(s).
Task lighting is already broken out separately in the standard end-use
report, although if other zones had task lighting then it would be comingled
with this process task lighting and not necessarily all process.
David
*
*
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
*Grumman/Butkus Associates*
*
*
*From:* Mark Darrall [mailto:MDarrall at a2so4.com]
*Sent:* Friday, May 27, 2011 2:41 PM
*To:* David Eldridge
*Cc:* equest-users
*Subject:* RE: Sizing runs in baseline model
Thanks, David. I could have been more clear. The sub-meter first came up
when we discussed our big exhaust hood / makeup air unit. They wanted to see
that energy shown as process energy. Later in the discussion, and this is
where my notes got fuzzy – task lighting and receptacle loads got mentioned
as process energy – I don’t know if they asked that those be put on the
sub-meter too or not.
Here’s what I’m looking at
Meter EM1-A is my sub-meter. All three dialogs are in the same zone. If I
switch “Task Lighting” and “Elec Equipment” to EM1-A, will eQUEST
automatically assign the numbers circled above to this meter? I can’t see a
way to assign loads to a meter within the zone internal loads dialogs…
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
[image: a2so4-email]
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL 317 388 8850
FAX 317 280 0692
MOB 765 749 0841
www.a2so4.com
*Please consider the environment before printing this e-mail*.
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
confidential and intended solely for the use of the individual or entity to
which they are addressed. If you are not the intended recipient, you may not
review, copy or distribute this message. If you have received this email in
error, please notify the sender immediately and delete the original message.
Neither the sender nor the company for which he or she works accepts any
liability for any damage caused by any virus transmitted by this email.
*From:* David Eldridge [mailto:dse at grummanbutkus.com]
*Sent:* Friday, May 27, 2011 3:22 PM
*To:* Mark Darrall
*Cc:* equest-users
*Subject:* RE: Sizing runs in baseline model
I think it shows up pretty clearly as “miscellaneous equipment” end-use in
the eQuest reports, so I’m not sure why they asked you about the submeter,
unless there was some inquiry about splitting up components of the process
load…I think it is an unneeded step, but you’ll have to work that out with
the reviewer as to why they asked specifically for it.
David
*
*
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
*Grumman/Butkus Associates*
*
*
*From:* Mark Darrall [mailto:MDarrall at a2so4.com]
*Sent:* Friday, May 27, 2011 2:05 PM
*To:* David Eldridge
*Cc:* equest-users
*Subject:* RE: Sizing runs in baseline model
Hi!
I got the unmet hours fixed in my baseline model. I think it had something
to do with the return air path – I had switched them from ducted to plenum
(to match design case because I didn’t see an App. G requirement for it) but
had them as unconditioned.
Back to the sub-metering question. I missed this in my discussion with the
review team –would it make sense to put ALL the process power on the
sub-meter as a way to directly see it? Seems that way to me. For our project
process power includes:
· Receptacles (office equipment and task lights)
· Refrigeration
· Cooking
I don’t think there are any difficulties in assigning these to the
sub-meter. I see there are places to directly assign them in the meter
properties – is there a risk of duplicating / double-counting them if
they’re also entered at the zone / system inputs?
Thanks, all. Have a great Memorial Day weekend and take a moment to thank a
Vet!
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 214 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 614 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 605 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 30394 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 618 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 33832 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1959 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 49415 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2061 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110528/f2364a6e/attachment-0011.jpeg>
More information about the Equest-users
mailing list