Direct solution: Define the constructions that space's surfaces
reference using layers that have mass. Entry with only U-value =
weightless.
Otherwise: I think this message is telling you eQuest can't figure out
how heavy the contents of the room (surfaces, furniture, etc...) are,
and is therefore assuming 70lb/ft2. You could just accept that
assumption if it's reasonable for your project.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian
Lo
Sent: Friday, November 11, 2011 1:15 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Delayed wall warning
I go the message:
custom weighting can not be calculated for SPACE EL1 Core Plnm (B.C43)
has 0 delayed walls, 1 delayed floors and 0 delayed ceilings. There
should be at least a delayed wall and floor, a delayed wall and ceiling,
or a delayed ceiling and floor for custom weighting factors to be
calculated. ASHRAE weighting factors with floor weight of 70 lb/ft2 (342
kg/m2).
How can i fix this problem?
Thanks
Brian
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111111/eedc7f4c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111111/eedc7f4c/attachment-0002.jpeg>
More information about the Equest-users
mailing list