[Equest-users] eQuest Workaround for Water Economizers
    Edward Allen 
    eallen at long.com
       
    Mon Nov 21 08:46:39 PST 2011
    
    
  
Kathiresan,
You could also then reference the separate model as a parametric run in your original model.
Edward M. Allen, P.E. CEM
Senior Energy Engineer
LONG Energy Solutions
M:720.217.1356
O:775.657.9180
----- Reply message -----
From: "Steven Savich" <ssavich at systemswestengineers.com>
To: "cic at jci.com" <cic at jci.com>
Cc: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQuest Workaround for Water Economizers
Date: Mon, Nov 21, 2011 8:33 am
Kathiresan,
I don't think you can do a parametric run of a water economizer chiller in the way you describe.  As I noted in my response to Tom a couple years ago, you'll need to define a *separate* water economizer chiller, condenser loop, and cooling tower *in addition to* the other chiller(s), loop(s), and cooling tower(s).  This will probably be more successful if you generate a separate model to compare to your baseline rather than attempt it as a parametric run.  Have a look at the equest/DOE new features manual at the section on “water economizer chillers”.
If you continue to run into problems, I recommend posting your .inp and .pd2 files to the equest users list.  For any given modeling problem, odds are there's at least one person on the list who's worked out a defensible/sensible method of handling the problem.
Good luck,
Steven
From: Kathiresan.Rajagopal at jci.com [mailto:Kathiresan.Rajagopal at jci.com] On Behalf Of cic at jci.com
Sent: Monday, November 21, 2011 5:10 AM
To: Steven Savich
Subject: Re: [Equest-users] eQuest Workaround for Water Economizers
Dear Steve,
I am trying to do parametric run for water economizer chiller just by changing water economizer from elect cent chiller. But it seems i am not getting any result. It seems i am missing lot of inputs.
Can you please put some important points needs to be taken care when modeling water economizer.?
Thanks for your advice
regards
Kathiresan
From:
"Steven Savich" <ssavich at systemswestengineers.com>
To:
<Tom at NorthernArchitects.com>
Cc:
equest-users at lists.onebuilding.org
Date:
09/18/2009 09:44 PM
Subject:
Re: [Equest-users] eQuest Workaround for Water Economizers
________________________________
Tom,
In the equest/DOE new features manual, there’s a section on “water economizer chillers”
Basically, to run a cooling tower in water economizer mode, you have to define a (virtual) water economizer chiller and attach a cooling tower & condenser water loop to it.  You’ll need to set up the water econ chiller, water econ condenser loop, and water econ cooling tower as  *completely* separate entities from any other chillers & cooling towers that you run and have them attached to the primary chilled water loop in parallel with the other chillers.
You also may need to use schedules, equipment controls, and load management of the chillers and circulation loops depending on your exact plant configuration.
For the water econ info, look under help/DOE2 help/Volume 6: New Features/Chiller Water Economizer
Hope this helps,
Steven
Steven Savich, LEED AP
Systems West Engineers
411 High Street
Eugene, OR  97401-2427
(541) 342-7210
(541) 342-7220 (fax)
________________________________
From: Tom O'Brien [mailto:Tom at NorthernArchitects.com]
Sent: Friday, September 18, 2009 7:56 AM
To: ssavich at systemswestengineers.com
Subject: eQuest Workaround for Water Economizers
Steve -
I read your eQuest post today today regarding your campus chilled water system / local cooling tower question.  I'm afraid I don't have a suggestion as I've not progressed that far with eQuest.
However, you noted that "I’m familiar with the equest workaround for water economizers".  We've been stumped by this in trying to set up a cooling tower / chiller combination that lets the cooling tower act as a precooler for the air-cooled chillers and/or as the cooling source when the building needs cooling in the winter months (our winter months are plenty cold enough to handle the relatively low cooling needs we have with a cooling tower without running the chillers).  eQuest doesn't seem to have a way to allow us to connect both the chillers and the cooling tower to the chilled water piping.  The typical eQuest cooling tower seems to want to connect to the condenser water off the chillers and assumes the chillers are water-cooled.
Can you point me in the right direction to find the find the workaround you mentioned?
Many Thanks.
Tom
Tom O'Brien
Northern Architects, Inc.
207 King Street Suite 3
Burlington, VT 05401
T: 802-658-1953
F: 802-658-2975
E: Tom at NorthernArchitects.com_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Equest-users
mailing list