[Equest-users] G3.1.3.14 Fan Power
    Rob Hudson 
    rdh4176 at gmail.com
       
    Wed Nov 30 07:24:23 PST 2011
    
    
  
G2.1.2.14 Fan Power (Systems 6 and 8). Fans in parallel VAV fan-powered
boxes shall be sized for 50% of the beak design flor rate and shall be
modeled with 0.35 W/cfm fan power.
Hope this helps.
On Wed, Nov 30, 2011 at 7:53 AM, <omoltay at mimtarch.com> wrote:
> Dear All,
>
> What is the correct fan power for VAV PFP systems? My printing of Appendix
> G has 03.35 W/CFM, which is definitely a misprint.
>
> Thank you,
>
> Omer Moltay
> Mimta
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111130/c5bd6702/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list