Either create multiple primary CHW loops (as is probably the case for a
building with so many chillers) or combine the chillers in a way that
makes the most modeling sense. With so many chillers, it will be
important to understand how they are (or will be) staged to meet the
load, and to combine their capacities, and prorate their efficiencies
etc. accordingly.
Regards,
Bill
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kimberly Wiebe
Sent: Friday, September 30, 2011 3:48 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] more than 10 chillers
Hello,
A building has 42 air cooled chillers. The maximum number of chillers
that be attached to the primary chw loop is 10. What do you do?
Kimberly Wiebe
Graduate Mechanical Engineer
Buro Happold
801 West Adams Suite 800
Chicago, IL 60607
USA
Tel: (+1) 312.451.1615
kimberly.wiebe at burohappold.com
www.burohappold.com
This message has been scanned by MailController -
portal1.mailcontroller.co.uk |
This message has been scanned by MailController
<http://portal1.mailcontroller.co.uk/> .
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111003/2fb5f0dc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111003/2fb5f0dc/attachment.jpeg>
More information about the Equest-users
mailing list