[Equest-users] 90.1-2007 Table 7.8 Water Heater Efficiencies
Kushagra Juneja
kce4 at kamalcogentenergy.com
Tue Oct 4 22:13:02 PDT 2011
Hi Paul,
There are two things being talked about, one is thermal efficiency and the
other is standby loss. Standby loss represented as (Q/800+110 SqRt V) and
thermal efficiency represented as 80%. I had the same doubt a while back. If
you look at other Formulae they are represented in the same way. Like for
instantaneous water heaters Energy Factor is given by 0.62-0.0019V. Btu/h is
the unit for Standby Loss. Not a multiplication factor. Hope this helps.
Cheers
Kushagra
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Tuesday, October 04, 2011 5:07 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 90.1-2007 Table 7.8 Water Heater Efficiencies
Could anyone help me understand the calculation for the minimum efficiency
of gas storage water heaters per the table above?
The calculation is 80%Et (Q/800+110 SqRt V) SL, Btuh.
I understand that Q is the nameplate input rate in Btuh and V is the volume.
Do I use the volume of the whole system, the storage tank only or the
recovery rate volume?
I understand SL is the standby loss. Does SL, Btuh mean multiply the
equation in parenthesis by the standby loss in btu's per hour?
Thanks for the help,
Paul Diglio
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111005/5c70d7ac/attachment-0002.htm>
More information about the Equest-users
mailing list