[Equest-users] Using global parameters to streamline modeling
Robby Oylear
robbyoylear at gmail.com
Fri Oct 14 08:13:29 PDT 2011
Dane,
What I'm discussing is in the Detailed Edit mode. Part of our efforts to
streamline energy modeling has been to stay out of the wizard as much as
possible. We mainly just use the wizard to setup the building shell, define
slab penetrations, and infiltration rates (i.e. things that are hard to do
in detailed edit mode).
Under the Building Shell tab in, select any space within your project.
C-ACTIVITY-DESC is located here:
[image: image.png]
We use a three letter acronym to describe the space type. In the example
above this space is a corridor. You can then create conditional statements
for most of the Space and/or Zone parameters based on this acronym.
For example, a user default expression for equipment W/SF can be written as
such:
if(#L("C-ACTIVITY-DESC")=="COR")
then (0.25) else
no_default
endif
These statements can have varied levels of complexity due to the nature of
referencing the different variables in eQUEST using the #BDL functions. For
instance, in the above example I'm referencing the local BDL keyword
"C-ACTIVITY-DESC" by using the BDL function #L which references a local BDL
keyword.
Hope this helps,
*Robby Oylear, LEED**®** AP BD+C*
*Mechanical Project Engineer*
*Energy Analyst*
* *
*D* 206-788-4571 | *C* 206-354-2721
*www.rushingco.com* <http://www.rushingco.com/>
On Fri, Oct 14, 2011 at 5:58 AM, Dane Heimerman <daneh at mlnai.com> wrote:
> Robby,
> Could you go over the basics of this C-ACTIVITY-DESC? I stumbled upon this
> thread, and it intrigued me, but I can't find what you're talking about.
> Where is 'space parameters'? Is this within the schematic of DD Wizard, or
> in detailed mode? If you could just get me pointed in the right direction,
> I'm usually able to struggle through it and learn on my own.
>
> Thanks,
>
> Dane Heimerman, EIT
> HVAC Engineer
> Michael L. Norris & Associates, Inc.
> 270 Walker Dr, Suite 201B
> State College, PA 16801
> p:814.867.3823
> f:814.867.4823daneh at mlnai.com
>
>
> On 10/13/2011 6:05 PM, Robby Oylear wrote:
>
> Bill,
>
> When I look at most of my project files, the Global Parameters list is
> pretty standard, however each parameter is usually project specific, i.e.
> Number of Residences, Glazing Ht by Orientation, System Efficiencies.
>
> One thing that can really help speed up modeling is to get fancy with the
> user-defined defaults, using basic IF/THEN statements you can setup default
> schedules, lighting w/sf, equip w/sf, infiltration etc. based on a trigger
> of the space.
>
> Using the C-ACTIVITY-DESC command under the Space Parameters you can
> label a space based on use, and have your defaults do the rest of the work
> for you.
>
> -Robby
>
> On Thu, Oct 13, 2011 at 1:11 PM, Bishop, Bill <wbishop at pathfinder-ea.com>wrote:
>
>> Does anyone use pre-defined global parameters in an input file that they
>> import, as a way to streamline the modeling process?
>>
>>
>>
>> I already have ASHRAE schedules and building constructions in an input
>> file that I import, but I never use global parameters.
>>
>> I make most of my universal changes by using User-Defined Default Values.
>> Am I missing a big opportunity to speed up the modeling process?
>>
>>
>>
>> Thanks,
>>
>> Bill
>>
>>
>>
>> [image: Senior Energy Engineer]
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111014/ff063e23/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 36090 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111014/ff063e23/attachment-0002.png>
More information about the Equest-users
mailing list