[Equest-users] Cooling capacity smaller than demand
Raczka, Karina
raczkak at AHA-Engineers.com
Tue Oct 25 11:25:06 PDT 2011
I just got a similar error message.
**WARNING**********************************************************************
Loop: DEFAULT-HW heating capacity is smaller
than the secondary demand. Primary= -1605200.
Secondary= -2199001.
My warning message popped up directly after I altered the pump energy and pump flow for my design HW pump (secondary demand). That means that I knew there was something wrong with my boiler capacity (primary demand). I adjusted it to what it should have actually been and the warning message disappeared accordingly.
I hope the help isn't too delayed for you.
Karina Rączka
LEED
A|H|A Consulting Engineers
24 Hartwell Ave, Third Floor, Lexington MA, 02421
781-372-3126 (p) : 781-372-3100 (f)
http://www.aha-engineers.com <http://www.aha-engineers.com/>
Karina_Raczka at aha-engineers.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Blue
Sent: Tuesday, October 11, 2011 3:51 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cooling capacity smaller than demand
I'm getting the following message:
**WARNING**********************************************************************
Loop: Condenser Water Loop cooling capacity is smaller
than the secondary demand. Primary= 2500000.
Secondary= 3344880.
Can anyone put me on the right track to figuring out where this secondary demand number is coming from (or has anyone dealt with this error before)? Nothing I'm doing to the building cooling coil capacities or configurations seems to change that secondary demand.
The primary capacity is that of the cooling tower.
I do have heat recovery on the attached chiller... maybe something to do with that?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111025/3a07cc6c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 9411 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111025/3a07cc6c/attachment-0002.jpeg>
More information about the Equest-users
mailing list