[Equest-users] COP used for simulation to fulfill LEED requirement

Joao Wong joao.wong at arup.com
Thu Sep 22 23:41:18 PDT 2011


Dear Jonathan,

As you mentioned, the chilled water supply temperature and the condensing for the baseline has been specified, hence, if you are using centrifugal chiller, the COP would be 6.1. The other table is for the statutory requirements for US.

For the proposed model, you should model explicitly on the equipment that will be installed.

Regards,

Joao Wong

Arup
Level 5  Festival Walk  80 Tat Chee Avenue  Kowloon Tong  Kowloon  Hong Kong
t +852 2528 3031  d+852 2268 3864
f +852 2268 3962
www.arup.com
P Please consider the environment before printing this e-mail

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mak, Jonathan Wai-Ho
Sent: Friday, September 23, 2011 14:28
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] COP used for simulation to fulfill LEED requirement

Dear all,

I am just simulating a project and wondering what the COP of the baseline model shall be.
Assuming the chiller is >1055kW, according to ASHRAE 90.1 Appendix G, the chilled water leaving temperature and condensing water entering & leaving temperature has been specified.
Shall I employ these data to determine the COP by Table 6.8.1J, i.e.  COP 6.1?
Because the chilled water and condensing water temperature in our project is differ from the ASHRAE standard, it seems that the COP cannot be compared in apple-by-apple.

Thanks so much for your kindly help.

Thanks,

Jonathan Mak

______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110923/0bd14820/attachment-0002.htm>


More information about the Equest-users mailing list