[Equest-users] Scale modeling
CleanTech Analytics
jeremiah at cleantechanalytics.com
Tue Apr 10 00:20:02 PDT 2012
Thanks I will keep that in mind..
I kinda enjoy the eQuest interface, so it is good to know there are
modeling tasks that it shines in! It has a nice parametric skylight tool
and good libraries, so will now be my tool of choice when skylights are
involved..
*Jeremiah D. Crossett*
*CleanTech Analytics*
*503-688-8951*
*www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
*
This document may contain valuable information proprietary to CleanTech
Analytics which is private and confidential. It may not be shared, copied,
stored or transmitted in any form without the prior written consent of
CleanTech Analytics
*
On Mon, Apr 9, 2012 at 11:05 PM, Stefano Moret <smoret at ucdavis.edu> wrote:
> Thanks all for your considerations, I much appreciate your
> recommendations.
> The nice thing about E-quest is that it support some elements, e.g.
> skylights, with many different features, while in Energyplus they are
> usually treated as normal windows.
>
> Thanks again, Cheers
> Stefano
>
> --
>
> Stefano Moret
> California Lighting Technology Center <http://cltc.ucdavis.edu/>
> University of California, Davis
> 633 Pena Drive
> Davis, CA 95618
>
> 530-747-3846
> smoret at ucdavis.edu
>
> On 09/apr/2012, at 18.28, CleanTech Analytics wrote:
>
> I had all to similar issues with eQuest, and and realized that eQuest is
> not really a reliable software. *I know the list is going to hate me.. The
> thing is that eQuest is deceptively easy, but when you want to find
> reliable results you basically have to find some "workaround"...
>
> The deal breaker for me in using eQuest for anything more then exploring
> early design options was:
>
> I had several real buildings complete with Energy Star portfolio manager
> data, as well as building audits, when I attempted to use eQuest discovered
> that eQuest was not capable of coming close to reality, in fact it wanted
> me to have something like zero insulation, and very poor U values to even
> come close. Given Energy Plus is not going to give exact results either but
> at least it comes close.
>
> Watch the lists, eQuest is full of "how do I come up with a work
> around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly
> "how does this feature work"
>
> I do not mean to insult eQuest users but my prospective is that it makes
> more since to use software that is harder to use, has better support and is
> updated regularly for such professional and high paid work, rather then the
> "workaround"
> Why eQuest is so popular is because it is easy, but for something like
> your project I suggest you use Energy Plus.
>
>
> *Jeremiah D. Crossett*
> *CleanTech Analytics*
> *503-688-8951*
> *www.cleantechanalytics.com* <http://www.cleantechanalytics.com/>
>
>
> *
> This document may contain valuable information proprietary to CleanTech
> Analytics which is private and confidential. It may not be shared, copied,
> stored or transmitted in any form without the prior written consent of
> CleanTech Analytics
> *
>
>
>
> On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret <smoret at ucdavis.edu> wrote:
>
>> Dear Nick,****
>>
>> ** **
>>
>> Thanks for your suggestions, I totally agree with your points, and I’m
>> conscious of the issues about the “generic guidelines”. I’m still surprised
>> by some unexpected results in my models though: I’ll work on my models to
>> try to understand the reasons leading to results which are different from
>> the measured ones.****
>>
>> ** **
>>
>> Thanks, Stefano****
>>
>> ** **
>>
>> *From:* Nick Caton [mailto:ncaton at smithboucher.com]
>> *Sent:* Monday, April 09, 2012 3:57 PM
>> *To:* Karen Walkerman; Stefano Moret
>> *Cc:* equest-users at lists.onebuilding.org
>> *Subject:* RE: [Equest-users] Scale modeling****
>>
>> ** **
>>
>> …I see my response is arriving too late to the conversation but here are
>> some further thoughts that might help Stefano and others:****
>>
>> ** **
>>
>> I have some parallel experience from which I can build/add to Karen’s
>> suggestions.****
>>
>> ** **
>>
>> I have performed studies with similar structure as Karen is suggesting
>> (creating and adding “building blocks” to evaluate building massing
>> options). However, for Stefano’s purposes I would caution to carefully
>> take stock of what questions you are trying to answer and whether an energy
>> model is really the way to go about finding those answers. ****
>>
>> ** **
>>
>> Using an energy model to develop generic guidelines with “arbitrary”
>> buildings/spaces for something inherently
>> site/climate/building-geometry-specific (such as “ideal window wall ratio”
>> or “ideal window properties”) is actually a terribly complex endeavor, as
>> I’m sure you are appreciating. You can ultimately come up with a set of
>> guidelines/spreadsheets/principles to use, but applying such developed
>> guidelines to an actual project for decision-making will always be fraught
>> with accuracy disclaimers (perhaps that is not the ultimate goal – I’m
>> only throwing this out for consideration). ****
>>
>> ** **
>>
>> Guidelines built around generic conditions are indeed useful and have
>> their place (ASHRAE’s advanced energy design guides are worth reviewing if
>> you’re at the outset of trying to find such results), but should only be
>> relied upon in the context of “I don’t want to invest in a site-specific
>> study and the increased accuracy / differing suggestions that may
>> produce.” Evaluating how well any study applies to the project-at-hand is
>> something to always keep in mind.****
>>
>> ** **
>>
>> To cut myself off: I think my response drafted so far is falling away
>> from Stefano’s original question as he’s more recently clarifying it, but
>> I’m ultimately driving towards furthering Karen’s first line: Build
>> project-specific models where you need a project-specific answer.****
>>
>> ** **
>>
>> To Stefano’s issue of scaling – I am nodding my head vigorously as you’re
>> observing how spaces modeled in isolation do not always additively
>> represent a group of spaces modeled together. It’s possible for that to
>> happen under certain circumstances, but the variables in play do not
>> normally scale linearly between an isolated space and a whole building
>> (consider the ratio of envelope surface area to conditioned volume, for one
>> instance). A big part of “big picture” modeling differences when compared
>> to “the smaller parts” is the tempering of various loads across spaces and
>> the way that has energy saving effects on HVAC systems in particular . *
>> ***
>>
>> ** **
>>
>> I would not spend too much time deliberating on such (expected)
>> differences, and would emphasize focusing on the results of isolated or
>> “whole building” models as appropriate to the purpose of your study =).**
>> **
>>
>> ** **
>>
>> ~Nick****
>>
>> ** **
>>
>> [image: cid:489575314 at 22072009-0ABB]**
>>
>> * *
>>
>> *NICK CATON, P.E.*
>>
>> SENIOR ENGINEER****
>>
>> ** **
>>
>> Smith & Boucher Engineers****
>>
>> 25501 west valley parkway, suite 200****
>>
>> olathe, ks 66061****
>>
>> direct 913.344.0036****
>>
>> fax 913.345.0617****
>>
>> www.smithboucher.com* *****
>>
>> ** **
>>
>> *From:* equest-users-bounces at lists.onebuilding.org
>> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Karen
>> Walkerman
>> *Sent:* Monday, April 09, 2012 4:18 PM
>> *To:* Stefano Moret
>> *Cc:* equest-users at lists.onebuilding.org
>> *Subject:* Re: [Equest-users] Scale modeling****
>>
>> ** **
>>
>> The short answer is that every building is different, and there is no
>> "typical" model that will fit them all.****
>>
>> ** **
>>
>> As you mentioned, the ratio between lighting/cooling/heating changes
>> depending on the size of the building. I'm willing to guess that this is
>> because the core zones that have very little need for heat get much larger
>> in relation to the perimeter zones. Also, the building energy needs will
>> change depending on orientation and global location.****
>>
>> ** **
>>
>> I would suggest that you take a slightly different approach - try to come
>> up with values that are representative for different types of spaces. You
>> might do say:****
>>
>> ** **
>>
>> 1. A perimeter office space with XX% glazing (run for North, East, South
>> and West exposures)****
>>
>> 2. A core office space with no skylights****
>>
>> 3. A core office space with XX% of roof area as skylights****
>>
>> 4. A core manufacturing space???****
>>
>> 5,6,7....****
>>
>> ** **
>>
>> Run each model in the applicable climate. Then, if you have an office
>> building that is 70% core and 30% perimeter space, you'll have a better
>> understanding of the building. This is still a very rough approximation,
>> but should get you farther than trying to model one "typical" building.**
>> **
>>
>> ** **
>>
>> --****
>>
>> Karen****
>>
>> ** **
>>
>> ** **
>>
>> On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret <smoret at ucdavis.edu> wrote:
>> ****
>>
>> Dear all,****
>>
>> ****
>>
>> I've recently played around quite a bit with E-quest to simulate the
>> effect of dynamic fenestration on building energy consumption. ****
>>
>> For these simulations I've been using a very simple office model with a
>> skylight on the top as a test-bed for my calculations (with default system
>> for HVAC and daylighting controls with dimming for lights) but, observing
>> the values I'm obtaining in output, I see that the values I obtain for
>> lighting, cooling and heating consumption make sense relatively, i.e. if
>> compared to themselves in different conditions, but are sometimes of
>> totally different order of magnitude if compared to each other
>> (lighting/cooling loads are often much higher than heating, by orders of
>> magnitude), especially when scaling up the model to bigger sizes. This way,
>> it's very difficult to see the effect of a variable change on the total
>> energy consumption. ****
>>
>> ****
>>
>> I know the model I'm using is very idealized, but is there any variable
>> that I can act on in order to obtain a model which has energy consumption
>> values more similar to a real building? For example, is there a "suggested"
>> size of the building that gives better results? Or maybe simulating a
>> single room in a large building gives more realistic results than the
>> single room alone? ****
>>
>> My point is that I would like to have a model whose results in scale
>> might be consistent when applied to bigger buildings. ****
>>
>> ****
>>
>> Thanks for your hints and suggestions, ****
>>
>> Stefano****
>>
>> ****
>>
>> --****
>>
>> ****
>>
>> Stefano Moret
>> California Lighting Technology Center <http://cltc.ucdavis.edu/>
>> University of California, Davis
>> 633 Pena Drive
>> Davis, CA 95618****
>>
>> 530-747-3846
>> smoret at ucdavis.edu <smoret at ad3.ucdavis.edu> * ***
>>
>> ****
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>>
>> ** **
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120410/6d2554e4/attachment-0002.htm>
More information about the Equest-users
mailing list