[Equest-users] Parallel Boxes for Packaged RTU
R B
slv3sat at gmail.com
Wed Apr 25 09:06:45 PDT 2012
Use Powered induction for the system type, and in the cooling source under
the cooling->coil capacity/control tab cool source as electric DX. If
eQuest is not allowing that, maybe you don't have the latest version
(actually this has been possible for quite some time).
-Rohini
On Wed, Apr 25, 2012 at 10:00 AM, Caleb Freeman <calebsfreeman at gmail.com>wrote:
> I am modeling an ASHRAE system type 6 and cannot seem to get equest to
> model this system type. I have tried to user override the VAV to parallel
> but that does not work. The default expression is set up to only allow
> parallel piu boxes for a piu system, but the only available piu system type
> is chilled water. Any suggestions to override the VAV box type or the
> system type to DX from CHW would be helpful.
>
> Thanks in advance,
>
> Caleb
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/384d4546/attachment-0002.htm>
More information about the Equest-users
mailing list